What if you were the inspector for this job?
You show up for the final electrical inspection.
The room walls and ceiling are finished and painted. (Not that you would particularly care if they were painted or not.)
Floor is bare concrete poured on grade.
You notice vinyl base is installed around the walls of the room at the wall to concrete floor.
You ask the electrician what is the intended purpose for the use of this room?
Response, for the grooming of the property owner's show dogs?
Bare concrete floor.
Will the concrete floor be washed down using water and a mop?
Will the bare concrete soak up water when it is washed?
As an electrical inspector in LA CA there is a good chance you will know the LA building codes if steel wire or rebar is required in the concrete slab pour.
Receptacles in the room are not GFCI protected.
Just curious would you pass the non GFCI protected receptacle outlets or flag, fail, the final inspection telling the electrician the outlets need to be GFCI protected?
NEC 210.8(2)&(6)
http://www.arpnjournals.org/jeas/research_papers/rp_2016/jeas_0516_4215.pdf