Please give me a break, you've got to be kidding, leave the engineering to engineers, and what ever 'aghast' comments I can think of.
The GFP absolutely may be able to be coordinated with the branch circuit breakers. In fact, I don't think I have never been able to coordinate with 30A, and some times higher, branch devices.
Right, but just because it is set at the minimum does not mean the solution is to turn it up. That is what has happend in this thread I think.