Would 2 sets of strings each feeding its own inverter but part of the same PV system be two arrays?
I really don't think so.
A "set of strings" to me could mean anything from one to...not sure. 12 strings into one combiner?
You could have two strings, one per inverter, or 12 strings, 6 per inverter- that's two inverters and ONE array to me.
"PV system" to me means everything connected to one AC combiner.
Say you have 320 panels(modules) wired in strings of 20, so 16 strings.
There could be (this is just hypothetical):
2 combiners / 8 strings each ---> one inverter (two input).
2 combiners / 8 strings each ---> two inverters (one or two inputs i suppose)
4 combiners / 4 strings each ---> four inverters
no combiners / 1 string per inverter = 16 inverters.
I'd call all 320 panels the "array" in all of the above, and the sections going to respective combiners "sub-arrays".
That way the sub-array is an "electrical sub-set", because it is going to separate inverters or inverter inputs or combiners.
It's a 'mechanically integrated assembly' of the components you'd expect.
My opinion: if you have two sets of modules that are sufficiently separated from each other that you need a raceway to support or protect the conductors between them,
Like you said, you have to look at every project, because there might not be any conductors going between strings. (I'm calling a set of modules a string here)
A string is electrically integrated, not mechanically integrated. They are two completely different things and speaking generally there is no telling how they will relate. One could have multiple strings per array or multiple arrays per string. You have to look at the individual project.
Blue for sure, but I really don't get how green would work.
A string could have a + connector in spot X, and the - connector from the opposite end of the string (electrically) could be 1 foot away, or 30 feet, or 100 feet from spot X.
But + or - (or both) have to be fused, so the + and - conductors from every separate string will be both electrically *and* mechanically connected in one or more fused combiner boxes?
Aren't all of the strings connected to a single inverter integrated in a way, in that it turns the whole bunch off if there is a problem with one?