bonding is about keeping all extranious-conductive-parts at the same potential.
Bonded (Bonding). Connected to establish electrical continuity
and conductivity.
bonding is about keeping all extranious-conductive-parts at the same potential.
i`m not on about the bloody connections...Bonded (Bonding). Connected to establish electrical continuity
and conductivity.
i`m not on about the bloody connections...
i`m on about the purpose it serves....and why so called `electricians` persistantly confuse bonding (either main or supplementary) with earthing...or what you call grounding...
the amount of times i`v heard folk refer to such stuff as `earth bonding`....it dont exist and it demonstrates a clear lack of understanding on what earthing...and bonding is...and the roles they play......
Maybe I am missing your point. What I am talking about is the purpose as I understand it.
Effective Ground-Fault Current Path. An intentionally
constructed, low-impedance electrically conductive path designed
and intended to carry current under ground-fault conditions
from the point of a ground fault on a wiring system to
the electrical supply source and that facilitates the operation of
the overcurrent protective device or ground-fault detectors on
high-impedance grounded systems.
Probably because the NEC calls what is really a bonding conductor the "equipment grounding conductor"....
i`m on about the purpose it serves....and why so called `electricians` persistantly confuse bonding (either main or supplementary) with earthing...or what you call grounding...
whats this got to do with bonding?
lol...It prevents the situation you mentioned in the first place. You mentioned crossbonding two "parts" to prevent a difference in potential between them. Our equipment grounding conductor, which is really a bonding conductor, connects conductive parts that aren't supposed to be energized to the return of the power source. The return side of the power source is the grounded side, so that's why the confusing "grounding conductor" is used. So if that metal part gets energized, the power source is shorted out which trips the overcurrent device. We usually bond each item that isn't supposed to be energized (e.g. a metal electrical enclosure). We don't typically bond separately from one enclosure to another, because each one is safed buy the equipment grounding/bonding conductor in the power feed to that enclosure.
Some situations in the NEC may require equipotential bonding grids or "cross" bonding conductors (e.g. swimming pool and hot tub decks and all metal parts within 5' of them).
lol...
its caus where working to different regs mate....you work to the NEC....i work to BS7671
but the fact remains that there seems to be confusion between earthing and bonding conductors here....
the interconnections between earth rods to create a `grid` or `nest` is all about parrallel paths...
bonding is there to keep extranious conductive parts at a similar potential.....
extranious conductive parts are parts that do not form part of the electrical installation....but could provide a path to earth under fault conditions....
so it seems to me that theres some confusion thinking that the bonding is what we refer to in the UK as the CPC...circuit protective conductor...when in fact bonding is a totaly seperate issue...
to put it in context:
earthing limits the duration of a touch voltage
bonding limits the value of a touch voltage
Your CPC is our Equipment Grounding Conductor. In both cases the function is to bond the non-current carrying conductive parts back to the system grounded conductor to provide a fault clearing path....
so it seems to me that theres some confusion thinking that the bonding is what we refer to in the UK as the CPC...circuit protective conductor...when in fact bonding is a totaly seperate issue...
lol...nope...right way round mate...I should have welcome to the forum so welcome to the forum.
For the most part what we discuss here is the NEC not what happens on the other side of the pond.
Please help this non-engineer understand what you mean by what I highlighted.
I think that you have them reversed but please still explain.
so this would be metallic enclosures...such as dis-boards, busbar chambers and metal plate switches etc...It prevents the situation you mentioned in the first place. You mentioned crossbonding two "parts" to prevent a difference in potential between them. Our equipment grounding conductor, which is really a bonding conductor, connects conductive parts that aren't supposed to be energized to the return of the power source. The return side of the power source is the grounded side, so that's why the confusing "grounding conductor" is used. So if that metal part gets energized, the power source is shorted out which trips the overcurrent device. We usually bond each item that isn't supposed to be energized (e.g. a metal electrical enclosure). We don't typically bond separately from one enclosure to another, because each one is safed buy the equipment grounding/bonding conductor in the power feed to that enclosure.
Some situations in the NEC may require equipotential bonding grids or "cross" bonding conductors (e.g. swimming pool and hot tub decks and all metal parts within 5' of them).
indeed..You can't compare your distribution systems to ours, as there are a lot of differences. For the US, low voltage circuits (120V relative to ground) connected to earth will not trip our smallest (15A) overcurrent device in many cases (e.g. residential, where there is no building steel or other decent electrode). The electrode resistance to earth is too high. If you have an RCD or other leakage device that will trip at well under 1 amp, then earthing will provide that protection. We don't have RCDs on most of our circuits, so the fault/touch voltage duration would be infinite if the earth was the only path for fault clearing.
Your starting voltage to earth is double ours (240 -vs- 120). But even that or our next step up of 277V to earth most likely won't trip a 15A breaker on a earth electrode fault.
Connecting to earth is for systems or surges of much higher voltage, and to dissipate static charge build up.
The situation you keep describing (running a conductor between various metal items) would be more typical in our high voltage substations. That, in addition to metal grids in the dirt, and other things all work well when the voltages are quite high (well over 1 KV). Connecting our residential distribution systems (120V) to earth doesn't do a lot for safety. Connecting the raceways and enclosures to the electrical return path does.
The sad thing is, we call our bonding conductor (fault clearing conductor) an equipment grounding conductor.
The sad thing is, we call our bonding conductor (fault clearing conductor) an equipment grounding conductor.
but `stray voltage` is induced....from current carrying conductors in proximity...so you still need to dump it to earth...dont you...What is even sadder is I still see many still not knowing the differences even if we had different names for the mentioned items.
We really need, but will never see in any of our lifetime, is to not use grounded conductors as normal current carrying conductors, and we will see a big decrease in potential objectionable current and so called "stray voltages" in components not intended to carry current. This even applies to POCO use of a MGN network.
indeed..
so do all systems in the US rely on TT?
....
but `stray voltage` is induced....from current carrying conductors in proximity...so you still need to dump it to earth...dont you...
stray voltage appeares where there is no reference point...the further away from a reference point you are (such as the star point on a TX)...the more likely there will be a few volts potential between conductors that are both referenced at the starpoint.....if this makes sense...
(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4).
but `stray voltage` is induced....from current carrying conductors in proximity...so you still need to dump it to earth...dont you...
stray voltage appeares where there is no reference point...the further away from a reference point you are (such as the star point on a TX)...the more likely there will be a few volts potential between conductors that are both referenced at the starpoint.....if this makes sense...
i think that quotation may be to do with what we call `eddy current`...which can be induced in metallic enclosures where cables are using different entrys....for example one knockout is used for the phase...and another knockout is used for neutral...Yes and no. Most of the "stray voltage" and I put quotations around that for a reason, I am talking about is what many call voltage phenomena that they really don't understand. It could be from current carrying conductors in proximity to something, but for most NEC applications this doesn't happen because of the requirement in 300.3(B) which says:
Following that will ensure that magnetic fields around the conductors of a particular circuit will cancel one another limiting any induced current to other objects. So IMO that source of stray current is not much of a problem most of the time. What seems to be more easily overlooked is parallel paths for intentionally grounded current carrying circuit conductors to take, that is what makes up most of the "stray voltage" I am talking about and what seems to cause the most trouble and confusion. Any interconnection between those grounded current carrying conductors and other grounded objects beyond a single earthing point (generally at/near the source) are subject to introduce problems.