glennspark
Member
- Location
- Leeds
but current wants to go to earth....and the more parrallel paths you provide it with.....the better it gets...Yes and no. Most of the "stray voltage" and I put quotations around that for a reason, I am talking about is what many call voltage phenomena that they really don't understand. It could be from current carrying conductors in proximity to something, but for most NEC applications this doesn't happen because of the requirement in 300.3(B) which says:
Following that will ensure that magnetic fields around the conductors of a particular circuit will cancel one another limiting any induced current to other objects. So IMO that source of stray current is not much of a problem most of the time. What seems to be more easily overlooked is parallel paths for intentionally grounded current carrying circuit conductors to take, that is what makes up most of the "stray voltage" I am talking about and what seems to cause the most trouble and confusion. Any interconnection between those grounded current carrying conductors and other grounded objects beyond a single earthing point (generally at/near the source) are subject to introduce problems.
dont forget that voltage remains the same in a parrallel circuit....the currents divide proportionally through each resistor...