don_resqcapt19 said:[FONT="] I think that the point that Gmack is trying to make is the same one that Bennie made a number of times before his passing. The impedance of the fault return path for a second building with a 3 wire feeder is almost always less than that of a feeder with a 4 wire service. The feeder neutral will almost always be larger than the EGC for that feeder. If you have a 3 wire feeder and a bonding jumper at the second building the ground fault current is carried on the neutral back to the source. If you have an EGC that current is on the EGC back to the service main bonding jumper and then on the neutral to the source. The second path has a higher impedance and will change the opening time for the OCPD. Assuming that the wire sizes in Table 250.122 are adequate, the trip time change should not be of any consequence.
Don
[/FONT]
Yes Don, fine. But the shunt occurs at first building GC [distance]
But with a parallel "extra" path the others problems can and do occur.
Take a HO or "maintenance worker landing a "neutral on a ground bus at second building.
Or: neutral separation and load using 4wire EGC and branch EGC for "neutral"
A MBJ solves many issues IMO.
What advantage is there with a 4wire.
Lets install that 4wire in IMC.
How many parallel paths do we have?