grounding at detached garage
Gmack said:
It will not improve anything.
Under sized EGC's cannot do the job of a full size GC as we are relating to here.
Now wait a minute.
Undersized EGCs or properly sized EGCs?
Under sized EGCs are already an NEC violation.
EGCs need not be as large as the circuit conductors to be effective.
iwire said:
Now wait a minute.
Minimum sized EGC's are properly sized but are not as large as full sized GC's.
Thats what I mean.
A #8 copper minimum is properly sized as per 250.122.
Will it do the same job as a #3 GC at tripping the OCPD's?
Upstream and down. On a sevice or feeder? Or branch?
I dont think so. It cant.
Imagine if you will a Coax between the two structures for example. If this coax is commonly bonded (through whatever means) to the Grounded Conductors of each of these structures and the Grounded Conductor is lost at the second building, we have the coax shield trying to carry the unbalanced neutral current back to it's source, not a good option is it?
That can't really be a problem as this exact parallel path is require by code rules for services.
Don
Don
Do I detect some sarcasm? :D
Roger
roger said:
Stickboy, the problem is Parallel Neutral paths as has been stated many times in this thread. If there are no parallel paths there is no problem.
Roger
Can't be any different than a POCO losing a ungrounded conductor... I just feel that everyone here has a different opinion and no hard facts to support it... (as far as running 3 vs. 4 wires to a remote panel)
Gmack said:
1] First I will respond to an earlier post where you stated that a open neutral 4wire had the advantage because building #2 would be in effect "isolated".
A] Well where do you think all that "floating" neutral current is?
B] It is sitting righ back at you in building #2 GES and all branch EGC's, complements of your EGC run with your 4wire.
No, it's not. Read 250.32(B)(1):
250.32(B)(1) Equipment Grounding Conductor. An equipment grounding conductor as described in 250.118 shall be run with the supply conductors and connected to the building or structure disconnecting means and to the grounding electrode(s). The equipment grounding conductor shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. The equipment grounding conductor shall be sized in accordance with 250.122. Any installed grounded conductor shall not be connected to the equipment grounding conductor or to the grounding electrode(s).
The neutral is not to be connected to the EGC or to the GES at the remote structure, when the feeder includes an EGC.
So, I ask again:
georgestolz said:
Why are you concerned about a fault's interaction with any building's Grounding Electrode System?
Imagine a feeder with an EGC installed to a building, that is sized as large as the neutral in the feeder.
The EGC in question would clear faults equally as fast.
So, would you say it's equal? I wouldn't. The four-wire has an advantage.
If the neutral opens under normal operations (as in, no faults), then none of the metal connected to the electrical system would be energized.
In the three-wire scenario, all the exposed metal would become energized, because the neutral is connected to the EGCs at the sub-panel. All that unbalanced current is trying to find it's way back to the transformer. It will find paths through people to get back, if the opportunity presents itself.
In my mind, that's about the only advantage. But, neutrals open infrequently, IMO, so it is a small advantage. I've never heard of a fatality from an open neutral, either. But the theory is sound. ;)
George,
Again that can't be a real safety problem because that is how we install all of our services, and I have seen a lot more open neutrals on the line side of the service disconnect than on a feeder circuit.
Don
Stickboy, you still haven't backed up your claim that a 4 wire feeder "isn't" allowed In CT.
Roger
George, Again that can't be a real safety problem because that is how we install all of our services,
Are you saying that an open neutral is not a safety problem at the service?
Or
Are you saying that because that it is a safety problem at the main it is okay to have the same safety problem elsewhere in the system?
This sounds like the soldier that was looking for a Section 8. He keep telling his CO that the reason that he didn?t want to take the point because there was only one sniper out there and he wanted two or more to shoot at him at the same time or he wouldn?t take the point.
How many different discussions have we had about installing a Main Lug panel in the detached garage?
This main lug panel is fed with a three wire feeder and the bonding is not complete what will facilitate the opening of the overcurrent devices in the remote building?
ATTENTION INSPECTOR MEMBERS; How many main lug panels do you see that are not bonded in the remote buildings?
Before the point of attachment there isn?t much that the NEC can do about the ?open neutral? or any other safety issue but after the point of attachment the NEC rules apply. The idea is to have only one point on the system where this ?floating neutral? syndrome can occur, at the main.
I am glad to see that the 2008, to date, mandates the installation of the equipment grounding conductor and compliance to all of Part III instead of just 250.50.
This will help stop the installation of main lug panels that are not bonding the equipment grounding conductors for the branch circuits back to the source.
The are many electricians as well as inspectors that can?t understand the bonding requirements of the main lug panel at a remote building such as a detached garage as they are taught in the beginning that these panels do not bond the grounded and grounding together.
Then there are some that believe that when the equipment grounding is installed with the feeders that it is to land in the same terminal bar as the grounded (neutral) in the remote panel. Their thoughts are that this main lug panel is treated as service equipment and the equipment grounding conductor is to land with the grounded (neutral) at the service equipment.
They end up running the equipment grounding and the grounded (neutral) conductors in parallel and then no bonding jumper thus the equipment grounding conductors for the branch circuits in the main lug panel are not bonded back to the source.
In my ?opinion? the 2008 cycle takes out all of the guess work and makes it a lot simpler and safer.
Mike I have no idea whatsoever how you managed to drag in the MLO panel discussion here.
This 250.32(B) discussion applies equally to MLO as MB panels.
How would a change in 250.32(B) have an effect on your pet peeve of MLO panels in separate buildings?
As far as people not understanding bonding and grounding.....of course lets 'dumb down' the NEC so even the simplest of pinheads can get it.
Mike,
Or
[FONT=&quot]All I am saying is that the code is telling us that the conditions that are required for services is a hazard at a second building. It those conditions are really a hazard, they present the same hazard at both locations and the code rules need to be the same for both locations. The parallel paths the are a hazard at the second building are required to be created by the code rules at services. Also, in my experience and opinion, there are many more open neutral conditions that occur on the line side of the service disconnect than on the load side of it.
When the code tells us that the electrons change their behavior based on who owns them, I really begin to question the technical competence of the code.
This is a lot like the rule that requires a marker tape above service conductors that are trenched in, but does not require a maker tape for the same conductors installed in the same location using directional boring. The hazard of a future dig-in does not change based on the installation method, but the code is telling us that it does.
Don
[/FONT]
So, I ask again:
You didnt read or hear.
Your 4 wire GC and EGC are connected back at building #1.
An open neutral at building #1 will place building #1 and #2 with potential/ "floating neutral" syndrome.
Why George, listen this time, your EGC connected at #1 building is connected to your EGC bus at #2 building and all its branch EGC's and interior metal piping and all the rest of its GES.
Don is right. We dont have open neutrals "much" in panels [busbars some, yes] But not many main lugs.
But I have had to troubleshoot a boatload on the line side of a service. And a hell breaks loose when that happens. If you havent been there, well then you wont understand.
But your "thesis" on building #2 is in error.
Now as to your "very dangerous" question. "Why be concerned aboult a fault on a GES"
Think on this.
All interior metal water piping exposed can and is used [in other than residential which is still used also within 5 ft of meter], for/as part of GES.
Last time I looked interior metal water piping is part of a GES as per NEC.
It can and will become energized and as electricians we bond and jumper so that "FAULT CURRENT" on the GES will trip OCPD's.
THAT! is why Im concerned George.
You should be too. Your presumption in all of this discussion isnt based on experience. Quit "mis" quoting the NEC.
You got a long way to go yet.
Roger
Sorry you have to wait till monday.... have to make call to state inspector...wanna make sure I get it from the horses mouth :>
Or
I don't install main lug panels in remote buildings, they are always main breaker, fed from a 3 wire... with the ungrounded conductor bonded to the ground.... as if it were a seperate service...
Really? (Sarcasm)
An open neutral at the service is not relevant to our discussion, except for comparison purposes. The question was, "What is the advantage of a three wire feeder over a feeder w/EGC?" If the service neutral at building 1 opens, everybody's screwed anyway.
Gmack, my patience with your "you're an ignorant punk kid" comments is wearing thin. So, I will counter with a picture, maybe we're just not on the same page. Please, explain to me how this open neutral ahead of building #2 will energize the exposed metals connected to the electrical system.
Let's get this aspect settled, and we'll return to the other issue.
Thank you all for your input, any thoughts on the requirement for a main in the subpanel? PS, in our area, they do not want us to ground anything to the footer steel! Their argument is that the footer steel is insulated from the earth by the plastic visqueen under it!
George,
That drawing appears to show the grounded conductor connected to the grounding conductor at two points in violation of the code rules.
Don
careco1,
They are correct, if the concrete is not in direct contact with the earth, you can't use the re-bar as a grounding electrode.
(3) Concrete-Encased Electrode An electrode encased by at least 50 mm (2 in.) of concrete, located within and near the bottom of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm ( 1/ 2 in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means.
As far as a main, 225.30 requires a disconnect for the second building, and a main is the easiest way to do this.
Don