so how would we then deal with this kwired>>>>?
250.4A(5) Effective Ground-Fault Current Path. Electrical equip‐
ment and wiring and other electrically conductive material
likely to become energized shall be installed in a manner that
creates a low-impedance circuit facilitating the operation of the
overcurrent device or ground detector for high-impedance
grounded systems. It shall be capable of safely carrying the
maximum ground-fault current likely to be imposed on it from
any point on the wiring system where a ground fault may occur
to the electrical supply source. The earth shall not be consid‐
ered as an effective ground-fault current path
~RJ~
Is “safely carrying” defined in the NEC? If not, I’d contend that if the breaker trips with the “ground fault current path” (be it wire or raceway) still intact, the fault current was safely carried.