petersonra said:What makes you think the terminology is incorrect?
If the GES is connected to an AC supply, then then it becomes a measure of impedance, not resistance.
petersonra said:What makes you think the terminology is incorrect?
peter d said:petersonra said:What makes you think the terminology is incorrect?
If the GES is connected to an AC supply, then then it becomes a measure of impedance, not resistance.
georgestolz said:These could be reasons for using resistance over impedance. Resistance won't change, right?
davidv said:Don, Bob, Bryan, n other Gents,
I'm grateful for all your opinions however with regards to your views on the "earth issue" , they're useful but not "acceptable" to me.
davidv said:Don,
The earth is a source & sink for all energy forms, sizing its reaction depending on the energy coming to it, not a conductor. it is part of the whole energy circuit, currents can be returnedFor current to flow there must be a complete circuit, unless the earth is generating the current in question, it cannot be returned to the earth.
davidv said:Running an AC current ( like lightning ) through a straight wire would bring about a resistance R ,and a very weak inductance ( very very much smaller compared to the R ) , (too impractical to measure).
Something else happened to correct the problem. The phase to phase phase to neutral voltages are not affected by bonding or not bonding. Only the phase to ground and neutral to ground voltages are affected.What brought attention to these mistakes was the voltage fluctuations between secondary phase wires to neutral when under load, 170v to n, 100v to n... Once the bonding jumpers were installed the voltage to neutral stabilized.
davidv said:hello guys
Its meant for Mr Peter d, as an illustration to using ground "resistance" term