Is it legal to connect the neutral to the yoke of the receptacle where I don't have a ground in the box? Receptacle says "UL" so I'd imagine its legal to do so?



1618663594846.png


1618663647020.png
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
This was the case long time ago. If the circuit does not have the EGC in the box then it is OK. But if it does then I would use the four prong receptacle and cord end.
 

Greentagger

Senior Member
Location
Texas
Occupation
Master Electrician, Electrical Inspector
200.9, 200.10(B), 250.126
No , that receptacle is not designed to be terminated as you suggested.
 

480sparky

Senior Member
Location
Iowegia
So how do I ground the yoke if I don't have a ground in the box?

My point is: Without the strap, the yoke cannot be grounded. When the yoke isn't grounded, a metal cover can't be grounded. You then have exposed, non-current-carrying parts that aren't grounded.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
Hence why I ask. Green neutral, strap... I want to know if UL cares. Because if they do that UL listing would not be valid.

I am sure UL cares. All we know that UL stamp on the device could be home made.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
My point is: Without the strap, the yoke cannot be grounded. When the yoke isn't grounded, a metal cover can't be grounded. You then have exposed, non-current-carrying parts that aren't grounded.

Makes sense.

So I want to ask- is this receptacle actually UL listed?
 