LarryFine said:I just want every forum member to send me $10.
(Not really. I want $20)
How does it feel to want? :grin:
I don't know, if it were me I would read the thread (as painfull as it maybe) before I sent you any money.
Roger
LarryFine said:I just want every forum member to send me $10.
(Not really. I want $20)
rcarroll said:I read 3 pages of the other thread. That was enough. Maybe time to nip this one.
mayjong said:i would never pass this installation, because you can't show me it works...
iwire said:I am keeping my mouth shut and my $20.00. :grin:
iwire said:I don't think I have to show you it works.
We have done many jobs leaving blank plates in place of future dinning room fixtures.
2-251 Log #575 NEC-P02 Final Action: Reject
(210.70)
__________________________________________________ __________
Submitter: Alan H. Nadon, City of Elkhart, IN
Recommendation: Revise as follows:
210.70 Lighting Outlets Required. Lighting outlets, that provide illumination,
shall be installed where specified in 210.70(A), (B), (C).
Substantiation: As currently worded, only 210.70(A)(2)(b) requires a lighting
outlet to actually illuminate anything. The definition of a lighting outlet, in
Article 100 does not require anything more than a junction box with switched
conductors intended to be connected to a lampholder, light fixture, or pendent
light. A proposal has also been submitted to change or amend the definition of
lighting outlet. Proper illumination ensures safe movement for persons thus
preventing many accidents.
Panel Meeting Action: Reject
Panel Statement: The objective of the NEC is to provide the requirement for the lighting outlet. The requirements specific to illumination are in the building code.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
roger said:OK, I'm bringing the ROP where CMP 2 said they don't require fixtures (at least in these locations) to the table just to see how many will say that the CMP doesn't mean what they are saying.
Roger
LarryFine said:I just want every forum member to send me $10.
(Not really. I want $20)
mayjong said:from the other (neverending)thread
Quote:
Originally Posted by Jim W in Tampa
Good thing your not an inspector cause nec says blanks are ok
how does an inspector test the circuit? remove the plates and lick the wires?
i would never pass this installation, because you can't show me it works... i
" inspect" and i surelly can't "inspect" this installation....