Have Backstabs Improved?

Learn the NEC with Mike Holt now!

Have Backstabs Improved?

  • I have experienced the improvement.

    Votes: 1 1.2%
  • I think they are now as reliable as screw connections.

    Votes: 6 7.4%
  • I think they are now reliable and always were.

    Votes: 11 13.6%
  • I think they are good enough.

    Votes: 9 11.1%
  • I think they are still unreliable after the design change.

    Votes: 23 28.4%
  • I have experienced their unreliability.

    Votes: 36 44.4%

  • Total voters
    81
Status
Not open for further replies.

ohm

Senior Member
Location
Birmingham, AL
celtic said:
Why would the stabs melt in the first place?
Something a bit more is invovled for a bolted short to occur.




So use #14 and save even more.

Well if there is a string of daisy-chained back stabbed receptacles and someone plugs in an appliance with a dead L-N short every receptacle will be a prime candidate for series arc faulting because they all got stressed.

And, because almost every outlet in a new home must now be on AFCI, I just find it less expensive to do everything in #12 to reduce home runs & labor. We can't even do MWBC very much anymore.
 

ohm

Senior Member
Location
Birmingham, AL
ohm said:
Well if there is a string of daisy-chained back stabbed receptacles and someone plugs in an appliance with a dead L-N short every receptacle will be a prime candidate for series arc faulting because they all got stressed.

And, because almost every outlet in a new home must now be on AFCI, I just find it less expensive to do everything in #12 to reduce home runs & labor. We can't even do MWBC very much anymore.

I should have said the short would have to be on the end of the daisy chain in order to stress all the others.
 

steelersman

Senior Member
Location
Lake Ridge, VA
GUNNING said:
Backstab or hook?
first of all I've never seen any union guys wire residential. So that would pretty much eliminate them backstabbing as you can't backstab #12 which is the lowest generally speaking size wire that they would be using. Think about it. :)
 

steelersman

Senior Member
Location
Lake Ridge, VA
ohm said:
Well if there is a string of daisy-chained back stabbed receptacles and someone plugs in an appliance with a dead L-N short every receptacle will be a prime candidate for series arc faulting because they all got stressed.

And, because almost every outlet in a new home must now be on AFCI, I just find it less expensive to do everything in #12 to reduce home runs & labor. We can't even do MWBC very much anymore.
why does everyone always act like 08 code is what's is what's in effect accross the country? In VA it hasn't been adopted yet. And I'm sure in many other states also.
 

Mule

Senior Member
Location
Oklahoma
We dont wire houses, but do extensions,additions and remodels. 98% of the time we always use mid grade Spec outlets with back pressure plate connections which I really like. I always tell the customers that we install a recept that will last, not the .44 cent models.

Years ago while doing alot of resi, we pigtailed with #14 THHN onto the #12 circuit and did backstabs on general lighting recepts and then did hook connections in kitchens, bath's, and the garage. I dont know if that was code compliant or not, but that's the way we did it.
 

wirebender

Senior Member
Mule said:
Years ago while doing alot of resi, we pigtailed with #14 THHN onto the #12 circuit and did backstabs on general lighting recepts and then did hook connections in kitchens, bath's, and the garage. I dont know if that was code compliant or not, but that's the way we did it.



Not compliant.

210.19(A)(4)exc.1(c) 2008NEC

(c) Individual outlets, other than receptacle outlets,
with taps not over 450 mm (18 in.) long.
 

ohm

Senior Member
Location
Birmingham, AL
steelersman said:
why does everyone always act like 08 code is what's is what's in effect accross the country? In VA it hasn't been adopted yet. And I'm sure in many other states also.

True all jurisdictions haven't adopted the 08 Code but it's a safe assumption that they will, in the future. The tamper resistant receptacles are up in the $1.29 range and of much better quality than the orange box $.33 stuff, maybe that will cure the melted receptacle problem.

TR withstanding, I don't think I'll do the backstabbing trick. I'd rather hook or loop a $.33 recp than push into a $1 backstab...but we all have our opinions.
 

bikeindy

Senior Member
Location
Indianapolis IN
ohm said:
True all jurisdictions haven't adopted the 08 Code but it's a safe assumption that they will, in the future. The tamper resistant receptacles are up in the $1.29 range and of much better quality than the orange box $.33 stuff, maybe that will cure the melted receptacle problem.

TR withstanding, I don't think I'll do the backstabbing trick. I'd rather hook or loop a $.33 recp than push into a $1 backstab...but we all have our opinions.

The reason for receptacles melting is not the quality of the device and the TR's are basicly the same quality as before just with a "safety" function.

And while Indiana is on the '05 NEC we don't have to install AFCI's though many contractors do.
 

celtic

Senior Member
Location
NJ
ohm said:
...I just find it less expensive to do everything in #12 to reduce home runs & labor.
How's that?
Is there some local code that places a maximum number of devices on a given general lighting circuit in a dwelling unit in your area?
 

celtic

Senior Member
Location
NJ
steelersman said:
first of all I've never seen any union guys wire residential. So that would pretty much eliminate them backstabbing as you can't backstab #12 which is the lowest generally speaking size wire that they would be using. Think about it. :)

I think you haven't seen it all.
 

ohm

Senior Member
Location
Birmingham, AL
celtic said:
How's that?
Is there some local code that places a maximum number of devices on a given general lighting circuit in a dwelling unit in your area?

Our county limits us to 10 outlets (receptacles or lights) on #14 and 12 on #12 AND everything in the 08 Code , except the communication grounding bus near the meter.
 

ohm

Senior Member
Location
Birmingham, AL
bikeindy said:
The reason for receptacles melting is not the quality of the device and the TR's are basicly the same quality as before just with a "safety" function.

And while Indiana is on the '05 NEC we don't have to install AFCI's though many contractors do.

I agree it's not the quality it's the design. I just can't understand how they got listed. I was just wishing they improved the design, I hate pushing them back in the hole when they fall out.
 