Failure Modes for Screwed Connections and Sprung Connections
Failure Modes for Screwed Connections and Sprung Connections
I'm with Rob, there was no, "Never backstab" option. I really like Gunning's opinion on post #21.
Look at the surface area used on a backstab device, now compare that to a screwed terminal's surface area. The wiper on the backstab device is spring loaded. It is spring loaded by a metal that is susceptible to heat, a heat that can break the material down over time.
This is good summary of why I dislike backstabbing. My objection to backstabs is based on the nature of the failure mode. It is a cascade event due to the high susceptibility of the sprung metal connection to heat.
If the sprung metal connector is heated it becomes annealed and softens. This annealing action weakens the spring action and reduces the contact force. The reduced contact force increases the contact resistance and increases the power dissipated in the connection. The increased power dissipated in the connection raises the temperature of the sprung metal strip. Now it start all over annealing, weakening, dissipating and increasing the connection temperature until complete failure occurs.
Screw terminals are much less susceptible to a thermal failure due to not relying on a light weight spring connection with limited contact surface area. Screwed connections have significantly higher mass and contact surface increasing their thermal dissipation capability and reducing contact resistance.
Electrical connections heat up and it has nothing to do with the good work we do inside the wall. All it takes is device with a weak or damaged connection to be plugged into a receptacle. Even a moderate current can cause this connection in the PLUG to heat and the blades of the plug transfer the heat to our carefully wired receptacle. Because what is plugged into the receptacle, once we are gone, is out of our control even the best workmanship in backstabbing may not be enough to avoid a failure significantly earlier than would occur with a screwed connection.
I reject the conclusion that backstabbing and screw terminals are equally good based on the fact that some screw terminals fail as well. I accept that all connections will fail. The issue is which connection style is more robust AND is the weakest connection design robust enough.
With the higher susceptibility of the backstab connection to thermal runaway AND the demonstrated failures in the field, I find the argument against using backstabs compelling.
Whether to backstab or not is an individual judgment call as backstab connections are listed connections. This forum, at its best, is a way for us to discuss issues and make informed personal decisions with knowledge gained from our peers, and not just our own experience.
In my view, the understanding I gained from this forum has not been able to convince me that because the backstab connection is listed it is a connection that is good enough. My judgment tells me otherwise.