My question is about reducing the voltage of a transformer. What happened is, a heating company replaced a comercial root top unit. Heat and cool. The problem with Chicago’s electrical grid seems to be the imbalanced voltage. We have a 240 volt, delta, 3 phase service. The manufacturer of the equipment is Trane. The equipment has a VFD drive blower. The VFD can not take the unbalanced power. My solution was to intercept the the wires feeding the blower and connect them to a transformer. The transformer is a 5kVA, 240 delta primary with a 240 Y secondary. Now Trane is saying that the moter is not getting up to speed because it needs 208 Y. So, is there a way to get 208 out of this transformer? Meaning connecting the line side to different tap conductors, or any outer way?
The current readings are line side 125, 125, 215 phase to ground. 250, 250, 225, pause to phase. The Load side readings are, 140, 140, 140, phase to ground, 250, 250, 225, phase to ground.
Picture 1, is the transformer label.
Picture 2, is the scep sheet of the RTU
Pictures 3-6 are the technical label on the transformer. Sorry, but no matter what I did part of the label was unreadable, so I cut it up.
Thanks
Mike
The current readings are line side 125, 125, 215 phase to ground. 250, 250, 225, pause to phase. The Load side readings are, 140, 140, 140, phase to ground, 250, 250, 225, phase to ground.
Picture 1, is the transformer label.
Picture 2, is the scep sheet of the RTU
Pictures 3-6 are the technical label on the transformer. Sorry, but no matter what I did part of the label was unreadable, so I cut it up.
Thanks
Mike