I concur, but again I believe even those instances that cause an actual fire to be quite rare. Usually a lose connection of some sort will make itself known, which in my world is one of four things 99% of the time - faulty wire nut splice, faulty backstab, faulty connection to bus bar, and faulty breaker to bus stab connection. In the case of splices, usually the damage is contained to the junction box.
My experience also, and IMO good reason why connections/splices are supposed to be in junction boxes or where open conductors are allowed they must have clearances to other objects, like the connections to a service drop for example.
 
Well...I can't tell you how many remodel's I've done where after the sheetrock is pulled down, the newly exposed romex has been gnawed through by rodents exposing the bare conductors. Many a fire been started from rodent damage. They wouldn't be chewing through MC...
 
Well...I can't tell you how many remodel's I've done where after the sheetrock is pulled down, the newly exposed romex has been gnawed through by rodents exposing the bare conductors. Many a fire been started from rodent damage. They wouldn't be chewing through MC...

If they chew off insulation but conductors remain clean/dry and in free air, they can go for a very long time and never cause any trouble.

If you have rodents though they typically do this activity in fairly concealed spaces (obviously there is access large enough for them to use) and they not only chew off such insulation, they also nest in the same areas, deposit urine, fecies, etc., bring in other nesting materials that are usually combustible so the combination of all that increases the risk of starting a fire if a condition turns up that is able to produce any arcing, or even resistive heating because of conductivity being introduced between those exposed conductors.
 
The NFPA states that between 2010 and 2014 Electrical issues only caused 9% of all home fires, this includes appliances, cords, and electronics so that means premise wiring is pretty safe even if it's NM. :thumbsup:



Roger
 
Well...I can't tell you how many remodel's I've done where after the sheetrock is pulled down, the newly exposed romex has been gnawed through by rodents exposing the bare conductors. Many a fire been started from rodent damage. They wouldn't be chewing through MC...

Ok, so you didn't want to touch the smoke load issue with regard to PVC pipe, so now we're on to rodent damage? :p

I just don't see the issues you see. I think it's mostly imagined, to be honest. I see all kinds of hacked up stuff on a daily basis that never caused a problem simply because they managed to make a splice that didn't overheat and cause an issue.
 
The NFPA states that between 2010 and 2014 Electrical issues only caused 9% of all home fires, this includes appliances, cords, and electronics so that means premise wiring is pretty safe even if it's NM. :thumbsup:



Roger

Precisely. :thumbsup: I would wager a large amount of money that of that 9%, the overwhelming majority of those fires were caused by issues beyond the outlet aka portable and temporary wiring.
 
I will say I have seen 18 AWG zip cord used where 12 AWG NM should have been used and the insulation was so brittle that it crumbles when you flex it even the slightest - that is probably from overheating. But can't ever recall seeing NM cable doing anything similar undersized or even when not undersized I only see heating damage near weak terminations for just a couple inches, and that is about it for heat damage caused by the current within the conductors. Seen external heating damage a few times though, too close to something that normally does get hot.
 
I do not have a clue.

I just knew a little bit of that info and had that link, prolly from Don also.

IIRC, he is a fireman or something and could answer better than I.
I have never accepted fire and smoke as being a real world issue. Just part of the ongoing code fights between metal clad cables and raceways and non-metallic cables and raceways. When you step back and look at the finished and furnishings of the building as compared to the mechanical and electrical system, you soon understand that the mechanical and electrical systems are such a small part of the total fuel load, it really does not make much difference.
 
Precisely. :thumbsup: I would wager a large amount of money that of that 9%, the overwhelming majority of those fires were caused by issues beyond the outlet aka portable and temporary wiring.
The stats used to force the AFCIs into the code said that 40% of the electrical fires are caused by the fixed wiring of the building.
 
So is that statistic even believable? It seems wildly inflated to me.
Maybe they took 1000 or even 10,000 incidents, then found 40 that were caused by issues in fixed wiring, then picked 60 others at random and then said those 100 were what was evaluated:blink:

You know skew the evaluation results to fit their needs.
 
So is that statistic even believable? It seems wildly inflated to me.
So, if they meant 40% of the total 9% that would mean only 3.6% of house fires were caused by premise wiring, pretty low in my book.

And out of the 3.6% I'd say most were installation errors, not wiring itself.

Roger
 
So, if they meant 40% of the total 9% that would mean only 3.6% of house fires were caused by premise wiring, pretty low in my book.

And out of the 3.6% I'd say most were installation errors, not wiring itself.

Roger
If you were an AFCI manufacturer you think mentioning 3.6% to code making panels is as convincing at getting them to accept requiring installation of your product as mentioning 40%, even though you didn't clarify exactly what it is 40% of?
 
Maybe they took 1000 or even 10,000 incidents, then found 40 that were caused by issues in fixed wiring, then picked 60 others at random and then said those 100 were what was evaluated:blink:

You know skew the evaluation results to fit their needs.
The numbers came from the NFIRS (National Fire Incident Reporting System). These are the fire cause reports submitted by fire departments.
 
So, if they meant 40% of the total 9% that would mean only 3.6% of house fires were caused by premise wiring, pretty low in my book.

And out of the 3.6% I'd say most were installation errors, not wiring itself.

Roger
Depending on whose numbers you are looking at, the percentage of dwelling unit electrical fires attributed to electrical is between 9 and 15, but yes the number of those fires caused by the fixed wiring of the structure would be 40% of that.
 
If you were an AFCI manufacturer you think mentioning 3.6% to code making panels is as convincing at getting them to accept requiring installation of your product as mentioning 40%, even though you didn't clarify exactly what it is 40% of?
The AFCI people never said that their device could only prevent 40% of the dwelling unit electrical fires. They strongly implied that they could prevent the vast majority of them. Note that the original proposals pretty much said that the original branch circuit and feeder device could do what they now tell us that the combination AFCI can do....the only problem with that is that the combination device did not exist until some 13 years after the original proposals.
 
Depending on whose numbers you are looking at, the percentage of dwelling unit electrical fires attributed to electrical is between 9 and 15, but yes the number of those fires caused by the fixed wiring of the structure would be 40% of that.
But did they clearly state 40% of 9 to 15% or did they put more emphasis on getting that 40% in CMP's minds.

If you don't think about it long and hard enough and get that 40 stuck in your mind and forget that it is 40% of 9%, you aren't seeing things as they really are, and it sounds much more significant then it is.
 
But did they clearly state 40% of 9 to 15% or did they put more emphasis on getting that 40% in CMP's minds.

If you don't think about it long and hard enough and get that 40 stuck in your mind and forget that it is 40% of 9%, you aren't seeing things as they really are, and it sounds much more significant then it is.
The proposals in support of AFCIs never really brought up the 40% number. It is just a number that you can find when you research the same data that they used to get the AFCIs into the code. I believe the number was brought up in some of the comments on the proposals.
 
So, if they meant 40% of the total 9% that would mean only 3.6% of house fires were caused by premise wiring, pretty low in my book.

And out of the 3.6% I'd say most were installation errors, not wiring itself.

Roger

Right, but 40% of the 9% still seems high to me. I really doubt that 40% of so-called "electrical" fires (the 9%) are caused by premises wiring.
 
Right, but 40% of the 9% still seems high to me. I really doubt that 40% of so-called "electrical" fires (the 9%) are caused by premises wiring.
Certainly not conductors/cables, other then at a termination point that got hot for whatever reason. I hear a lot of emphasis put on undersized conductors at times - reality is I don't think that in itself causes as much trouble as many think, I think most the issues it does cause is at terminations, but if those are inside an enclosure like they are supposed to be - that greatly reduces fire hazard.
 