timceps said:Since all outlets in sleeping areas require to be AFCI. Does this include required smoke detectors which is life safety? Some Architects specify that they need to be powered freom dedicated bathroom Receptacle circuit.
C3PO said:If your smoke detectors were low voltage (like the ones some security people put in) then you would not have to AFCI protect them. Otherwise it is required.
lpelectric said:The requirement at 210.12 is for outlets (receptacles, lights, smoke detectors, paddle fans, etc.,) that are fed from 120 volt, 15 or 20 amp circuits, so low voltage would not apply to this rule. :smile:
gndrod said:Article 761.21 and 761.41 are applicable as 210.12 not permitted.
abe72487 said:However when asked I tell HO to install smokes on hallway circuit so if there is an incident they will still have power, not just battery backup. Never install smokes on their own circuit.
*However, some local regulations may alter that NEC-correct statement.peter d said:The alarms go "chirp" when the batteries get low. There is no reason, other than what the NEC and local code requires, that smokes can't be on their own circuit.
isn't in the 08 code that all circuits other than gfci protected outlets (small appliance, bathrm gfci and outside recepts, ect) have to be afci protected, so that would make all smoke alarms inside a bedroom or outside a bedroom in the hallway protected by afci.abe72487 said:I agree that smoke detectors are not part of a fire alarm system. However when asked I tell HO to install smokes on hallway circuit so if there is an incident they will still have power, not just battery backup. Never install smokes on their own circuit.
abe72487 said:If smokes are on dedicated circuit and it trips you would not know until the battery in smokes was loow enough to chirp. Not many people check their panel daily.
abe72487 said:If smokes are on dedicated circuit and it trips you would not know until the battery in smokes was loow enough to chirp. Not many people check their panel daily. I Idaho we are going to enforce the AFCI rule with 2005 NEC so only bedroom circuits would have AFCI protection.
csparkrun said:oregons addendum still applies that fire safety devices still not be afci protected
Sometimes breakers trip due to short circuits and ground faults.Tiger Electrical said:Why might such a lightly loaded dedicated circuit trip a breaker?