tajaj said:bozo died lastnight
Yes, he did.
Was the party going good when you heard about his death?
tajaj said:bozo died lastnight
iwire said:Your mixing products.
Smoke Detectors are not the same item as Smoke Alarms
Smoke Alarms are never part of a system.
They are stand alone and can be interconnected.
They are never covered by 760
On the other hand smoke detectors that connect to a panel are covered by 760
In some areas even if you have a fire alarm system with heats and smokes covered by 760 you will still have to install smoke alarms as the laws generally require smoke alarms in dwelling units and do not recognize smoke detectors.
dnem said:I don't see that "alarm" tells you if you're exclusively in a system or exclusively in a single station.
Single- and Multiple-station Smoke Alarms
(UTGT)
USE
This category covers single- and multiple-station smoke alarms intended to be employed in indoor locations where sensitivity testing and maintenance of alarms, per section 10.4.4 of ANSI/NFPA 72, ‘‘National Fire Alarm Code’’ (2007 Edition), is required by code, Authorities Having Jurisdiction, or other requirement.
This category also covers single- and multiple-station smoke alarms that have been performance tested to a minimum 10-year extended battery life under normal ambient conditions. Unless otherwise noted in the individual Listings, the alarms are intended for flush-mounted installation only, and are not intended for use on surface-mounted boxes.
ALARM TYPES
Single Station — Self-contained units that incorporate a smoke chamber,
an optional heat detector, and related electrical components to initiate
an audible alarm signal from the unit when abnormal smoke or heat
(when a supplementary heat detector is provided) actuates the unit. These
devices may be energized from a commercial power-supply source by
means of permanent wiring in accordance with ANSI/NFPA 70,
‘‘National Electrical Code,’’ flexible power-supply cord, use of limitedenergy
cable or equivalent wiring connected to the output of a suitable
Class 2 power supply, or by one or more batteries.
Where a battery is employed as the main supply, its depletion below
the level at which an alarm signal would be obtained is indicated by a
distinctive audible trouble signal which persists for at least seven days.
Multiple Station — Similar to single-station units but provided with leads
or terminals (or integral RF transmitter/receiver units) to permit the interconnection
of single-station units so that actuation of any one unit results in
actuation of the audible alarms of all units. The installation instructions
(manual) indicate the maximum number of units that can be interconnected.
Refer to Chapter 8 of ANSI/NFPA 72 and the instruction manual provided
with each smoke alarm for installation data. ANSI/NFPA 72 includes installation
requirements of fire warning equipment in family living units. This is
intended to cover living areas only and not common usage areas of multifamily
buildings such as corridors, lobbies, stairwells, etc.
Smoke-automatic Fire Detectors (UROX)
GENERALThis category covers detecting combinations designed to detect smoke
particles. Smoke detectors may or may not be designed to be connected
to fire alarm system control units (see APPLICATIONS).
A heat detector and/or an audible-signaling appliance may be provided
integral with the detector.
The primary function of duct detectors is to shut down the blowers
and/or dampers of air conditioning and ventilating systems in an attempt
to prevent a possible panic and smoke damage from distribution of
smoke. Duct detectors are not intended as a substitute for open-area protection.
The level of toxicity produced by the combustibles at which smoke
detectors actuate has not been investigated.
DETECTOR TYPES
Photoelectric (P) — Designed to detect an abnormal density of smoke
particles, either by obscuration of a projected light path or reflection of
light from the smoke particles onto a light-sensitive element.
Ionization (I) — An ionization smoke detector has a small amount of
radioactive material that ionizes the air in the sensing chamber, thus rendering
it conductive and permitting a current flow through the air
between two charged electrodes. This gives the sensing chamber an effective
electrical conductance. When smoke particles enter the ionization
area, they decrease the conductance of the air by attaching themselves to
the ions, causing a reduction in mobility. When the conductance is less
than a predetermined level, the detector circuit responds.
Combination Photoelectric/Ionization (P/I) — Employs both principles
of detection in one unit.
Projected Beam (PB) — A light beam is projected across the space of
area to be protected.
Air Sampling (AS) — Consists of air-sampling ports at the ends of piping
or tubing extending from the detector unit to the areas to be protected.
A pump draws air from the protected area through the ports and
tubing to the detector where the air is analyzed for fire products.
APPLICATIONS
Open-area Protection (OAP) — Requires detector connection to a compatible
system control unit for operation.
iwire said:David I really don't know what your asking.
I have posted the UL info, IMO a notification device is clearly not an 'alarm'.
dnem said:You posted UL info that said
Single- and Multiple-station Smoke Alarms
How about an alarm that is not Single- or Multiple-station ?