Jerramundi
Senior Member
- Location
- Chicago
- Occupation
- Licensed Residential Electrician
Am I right to think 250.64(C)(1) applies only to a single GEC and say, for example, splice onto it in order to extend it?That should be fine just keep in mind that your water pipe electrode must be supplemented by another electrode. See 250.53
... and that I SHOULD be looking at 250.64(D), in which 250.64(D)(1)(1) allows for taps to a common GEC to be simply "connectors listed as grounding and bonding equipment?"