per request, i have created yet another thread on this topic
references:
http://forums.mikeholt.com/showthread.php?t=178511
http://forums.mikeholt.com/showthread.php?t=180638
in essence, is using the test button on the GFCI really a good test? UL suggests that using 5-p tester is not all encompassing, NEMA suggests the use of a 5-p tester with a load applied, others say only the GFCI test button should be used. but we know that AHJ's use these 5-p testers that cannot verify GFCI function on 2-wire installs.
i also find it silly to allow a 5-r GFCI to be a 1-r GFCI when no EGC is there, the use of plastic EGC blockout should be used to convert the 5-r GFCI into a 1-r GFCI because the application was to GFCI a non-GFCI 1-r (replace the 1-r) and protect any downstream outlets. 406.4(D)(2)(b)
use of a sticker is kinda useless, and, if there was no hazard to be had using 5-r GFCI w/o EGC then why does NEC call for a sticker??
references:
http://forums.mikeholt.com/showthread.php?t=178511
http://forums.mikeholt.com/showthread.php?t=180638
in essence, is using the test button on the GFCI really a good test? UL suggests that using 5-p tester is not all encompassing, NEMA suggests the use of a 5-p tester with a load applied, others say only the GFCI test button should be used. but we know that AHJ's use these 5-p testers that cannot verify GFCI function on 2-wire installs.
i also find it silly to allow a 5-r GFCI to be a 1-r GFCI when no EGC is there, the use of plastic EGC blockout should be used to convert the 5-r GFCI into a 1-r GFCI because the application was to GFCI a non-GFCI 1-r (replace the 1-r) and protect any downstream outlets. 406.4(D)(2)(b)
use of a sticker is kinda useless, and, if there was no hazard to be had using 5-r GFCI w/o EGC then why does NEC call for a sticker??