110.14 Electrical Connections. Because of different characteristics
of dissimilar metals, devices such as pressure
terminal or pressure splicing connectors and soldering lugs
shall be identified for the material of the conductor and
shall be properly installed and used. Conductors of dissimilar
metals shall not be intermixed in a terminal or splicing
connector where physical contact occurs between dissimilar
conductors (such as copper and aluminum, copper and
copper-clad aluminum, or aluminum and copper-clad aluminum),
unless the device is identified for the purpose and
conditions of use. Materials such as solder, fluxes, inhibitors,
and compounds, where employed, shall be suitable for
the use and shall be of a type that will not adversely affect
the conductors, installation, or equipment.
110.14(A) Terminals. Connection of conductors to terminal parts
shall ensure a thoroughly good connection without damaging
the conductors and shall be made by means of pressure
connectors (including set-screw type), solder lugs, or
splices to flexible leads.
110.14(B) Splices. Conductors shall be spliced or joined with
splicing devices identified for the use or by brazing, welding,
or soldering with a fusible metal or alloy. Soldered
splices shall first be spliced or joined so as to be mechanically
and electrically secure without solder and then be
soldered.
230.81 Connection to Terminals. The service conductors
shall be connected to the service disconnecting means by
pressure connectors, clamps, or other approved means.
Connections that depend on solder shall not be used.
250.8 Connection of Grounding and Bonding Equipment.
250.8(B) Methods Not Permitted. Connection devices or fittings
that depend solely on solder shall not be used.
250.70 Methods of Grounding and Bonding Conductor
Connection to Electrodes. The grounding or bonding conductor
shall be connected to the grounding electrode by
exothermic welding, listed lugs, listed pressure connectors,
listed clamps, or other listed means. Connections depending
on solder shall not be used.
250.148 Continuity and Attachment of Equipment
Grounding Conductors to Boxes.
(E) Solder. Connections depending solely on solder shall
not be used
393.40 Connectors and Enclosures.
(A) Connectors. Connections to busbar grid rails, cables,
and conductors shall be made with listed insulating devices,
and these connections shall be accessible after installation.
A soldered connection shall be made mechanically secure
before being soldered.
394.56 Splices and Taps. Splices shall be soldered unless
approved splicing devices are used. In-line or strain splices
shall not be used.
410.54 Pendant Conductors for Incandescent Filament
Lamps.
(A) Support. Pendant lampholders with permanently attached
leads, where used for other than festoon wiring,
shall be hung from separate stranded rubber-covered conductors
that are soldered directly to the circuit conductors
but supported independently thereof.
410.121 Solder Prohibited. No solder shall be used in the
construction of a luminaire recessed housing.
520.43 Footlights.
(A) Metal Trough Construction. Where metal trough
construction is employed for footlights, the trough containing
the circuit conductors shall be made of sheet metal not
lighter than 0.81 mm (0.032 in.) and treated to prevent
oxidation. Lampholder terminals shall be kept at least
13 mm (1?2 in.) from the metal of the trough. The circuit
conductors shall be soldered to the lampholder terminals.
520.43 Footlights.
(B) Other-Than-Metal Trough Construction. Where the
metal trough construction specified in 520.43(A) is not
used, footlights shall consist of individual outlets with lampholders
wired with rigid metal conduit, intermediate metal
conduit, or flexible metal conduit, Type MC cable, or
mineral-insulated, metal-sheathed cable. The circuit conductors
shall be soldered to the lampholder terminals.
552.10 Low-Voltage Systems.
(C) Low-Voltage Wiring Methods.
(2) Splices. Conductors shall be spliced or joined with
splicing devices that provide a secure connection or by
brazing, welding, or soldering with a fusible metal or alloy.
Soldered splices shall first be spliced or joined to be mechanically
and electrically secure without solder, and then
soldered.
695.6 Power Wiring.
(D) Pump Wiring. All wiring from the controllers to the
pump motors shall be in rigid metal conduit, intermediate
metal conduit, electrical metallic tubing, liquidtight flexible
metal conduit, or liquidtight flexible nonmetallic conduit
Type LFNC-B, listed Type MC cable with an impervious
covering, or Type MI cable. Electrical connections at motor
terminal boxes shall be made with a listed means of connection.
Twist-on, insulation-piercing?type, and soldered
wire connectors shall not be permitted to be used for this
purpose.