I guess the biggest difference is that when I have a rooftop unit with a nameplate from the manufacturer, I have a piece of equipment with a hermetic motor in it, along with a bunch of other stuff, and that is what I am sizing for, not multiple motors, the type of which are covered in 430.
The other difference I see is that 430.24 refers you to 430.6 which applies to motors that are not hermetic compressors, and then refers you to a table that has you look up the HP of the motor and translate it into FLC to do your calcs. Hermetic compressor motors have rated load current on the nameplate and are not required to have HP marked. A packaged rooftop equipment could have redundant loads in it. Without the sequence of operations, you would not know that. All of these reasons are why 440 seems to tells us to use the equipment nameplate data for this type of equipment.
220.50 directs you to 430.24 for the calculation of motor loads for feeders and services.
430.24 tells you to take 125% of the largest motor (as determined by 430.6(A)) plus the sum of the full load currents of the other motors (as determined by 430.6(A)) as the load for several motors.
430.6(A) tells you that the current rating of the motor shall be determined by the Tables 430.247 thru 430.250.
440.6
MODIFIES the provisions of 430.6 when dealing with Air-Conditioning and Refrigerating Equipment. (If you recall we talked about how Art 430 applies to Art 440 equipment, except as modified by Art 440.)
440.6(A) says that the Rated Load Current of the compressor shall be used as the current rating (instead of the current rating from Tables 430.247 thru 430.250.)
440.6(B) says that the marked full load current of fans or blowers in Art 440 Equipment shall be used as the current rating (instead of the current rating from Tables 430.247 thru 430.250.)
So, imagine you had a 480V feeder supplying a 5HP pump, a 1HP fan, and a piece of Air Conditioning Equipment that had a 5HP compressor with an RLA of 6.5A and a 1HP blower with an FLA of 1.8A.
Per 220.50 and 430.24 (and 440.6) the load on the feeder would be:
5HP pump = 7.6A*1.25 = 9.5A
1HP fan
......................= 2.1A
5HP Comp
..................= 6.5A
1HP blower
.................=
1.8A
Total
.......................... = 19.9A
The MCA of the Air Conditioning Equipment (which would be 9.93A) does not figure into the load calculation for the feeder at all.