jjs
Member
- Location
- Puryear, TN, USA
I'd rather use the #3 feeder conductors for an actual current of 94.5A.
I just want to specify the amount that is going to work per the code. As an engineer, I am not paying for the #2 or #3, unless I specify the smaller amount and it is found out to not meet code, then I will have to pay for it, the client will be unhappy, someone can get hurt, and property damage can happen. So that is why it is important to me to get the code required size.
David, just curious if you are an engineer, electrician, code inspector, or something else?