There's absolutely no reason to run more than one IG conductor for one circuit, and one could even suffice for all IG circuits.If there is more than one IG receptacle on a branch circuit is a seperate insulated EGC reccommended for each device? Application is steel emt and thhn conductors.
Nope it would be a waste of materials. You are required to bond the EGC to the receptacle case case and yoke, thereby putting all EGC's in parallel or 1 great big conductor in parallel with the EMT. You do not even need the EGC if using EMT, all you need is the IG.If there is more than one IG receptacle on a branch circuit is a separate insulated EGC recommended for each device?
So you could install a jumper wire from the metal box to the "U" terminal on the IG recep and call it good?
You sure can, nothing in the NEC code would prevent it, only ethical code books frown on it.So you could install a jumper wire from the metal box to the "U" terminal on the IG recep and call it good?
It would be a good EGC, but it would no longer be an IG. The jumper would defeat (bypass) the IG receptacles insulated grounding terminal.So you could install a jumper wire from the metal box to the "U" terminal on the IG recep and call it good?
It would be a good EGC, but it would no longer be an IG. The jumper would defeat (bypass) the IG receptacles insulated grounding terminal.
Please define IG.![]()
Since I have never seen a definition of an IG in the NEC, I have always viewed an IG as an Isolated Ground path. Not a definition but perhaps a description.
Absolutely correct and hence is a design issue, not NEC.My point is there is no NEC standard to apply. The NEC simply gives us permission to run an 'IG' conductor back through j-boxes and panels without connection but does not require that.
The purpose of IG's is to reduce line noise in critical circuits.
The IG, Hot and Neutral wires should have a one to one to one relationship, all in close proximity to each other, all the way back to the service entrance.
This means:
If you Daisy Chain the Hots, then you Daisy Chain the Neutrals and IGs.
If you Home Run the Hots then you Home Run the Neutrals and IGs.
If you Home Run the Hots then you Home Run the Neutrals and IGs.
It seems that you would be defeating the purpose of the IG circuit by installing multiple outlets.
Problem is an IGR is not capable of reducing any noise. It has absolutely no passive or active circuits.The purpose of IG's is to reduce line noise in critical circuits.
Good question and the answer is pretty simple. If you have ever worked with electronic systems that use a DC rectifier of some type, and that is in every thing electronic powered by AC, manufactures have to meet FCC regulations to prevent radio frequency inference or RFI...Why?:-? I am curious.
Mr first answer wasn't very clear. Let's try:Problem is an IGR is not capable of reducing any noise. It has absolutely no passive or active circuits.
I do not ever recall installing multiple IG outlets on a circuit. It seems that you would be defeating the purpose of the IG circuit by installing multiple outlets.