- Location
- Windsor, CO NEC: 2017
- Occupation
- Hospital Master Electrician
That's three pages of fine print. What section forbids the installation?joe tedesco said:See Page 57 and beyond in the UL 2006 White Book for CONDUIT FITTINGS (DWTT)
That's three pages of fine print. What section forbids the installation?joe tedesco said:See Page 57 and beyond in the UL 2006 White Book for CONDUIT FITTINGS (DWTT)
joe tedesco said:PS: I have some really good violation pictures from Syracuse, NY, or should I say $$$ the crossed Neutral city?
roger said:When the listed connectors are installed on either, what the connector goes into is a completely different item.
Using your logic the enclosure the Listed Fitting goes into must be also be listed in the articles huh?![]()
Roger
Yes we do have to use some common sense here. A rigid coupling is a fitting with straight threads. The NEMA standards says the connectors can be used with some threaded items with straight threads. I see no problem when it is used with a coupling and I see nothing in the NEMA standard, the UL listing or the NEC that says it can't be used with a conduit coupling.You have to use some common sense here. Is a rigid coupling listed as a raceway? Or is it a coupling for a rigid raceway? It definetly isn't listed to couple EMT and FMC.
Is it your opinion, then, that NEMA standards and UL listings are permissive texts?don_resqcapt19 said:,,,I see nothing in the NEMA standard, the UL listing...
joe tedesco said:Ryan, I am surprised at your comments, you teach the NEC and proper use of the Code, and still will allow the misuse of fittings in violation of 110.3?