barbeer
- Pinellas County, FL
I am pretty sure that I did not see any anti-short bushings shown in that fancy NEMA thingy!? Anybody think of that?
barbeer said:I am pretty sure that I did not see any anti-short bushings shown in that fancy NEMA thingy!? Anybody think of that?
Rockyd said:Hillbilly,
(s)Lowes is not exactly the shining pillar of electrical knowledge in the industry. I think if you had all the code gurus standing pointing at it, it would be considered a violation. If they were out on a job, they'd do it in a heartbeat, and file it in the"it wasn't pretty, but had no options" closet that like everyone in this industry, has "some junk in the trunk".
I have no problem with it if it is made tight and secure, and has an EGC (wire) sized per 250-122.
Anyone have a NEIS book that covers this?
Is there anyone sitting on a CMP that wants to tackle it?
barbeer said:I was if fact thinking about the AC and MC cable aspect of the presentation, not the FMC since the presentation addressed all three!
barbeer said:NEMA(I know you are not a big fan from previously in the post) also says the NEC does not require anti shorts.
Do certain connectors require the bushings to achieve rating and certain ones they are not required. I do turn down a job where they are not used.
davet said:Q:If running metal conduits containing your wiring system with no seperate ground wire(using cinduits as ground.Ex:3 phase circuit,no neut.) and a short results in conduit,How many amps can the conduit run handle?
hillbilly said:I was standing in line at (s)Lowes the other day. While waiting, I look up and what do I see? A transformer installation using exactly the same parts as Joe's picture.
steve
I see a similar arrangement for suspended exit signs from time to time. I do the same installs, but with RMC or IMC down rods and jack chain for a safety chain on the exit signs. You can split a set screw fitting sometimes by cranking the set screw too hard sometimes. I certainly wouldn't want to rely on its mechanical strength to support something.Jacob S said:Steve's comment along with this entire thread has reminded me of a huge pet peeve of mine at every home depot I have ever been in. In my area, the stores use large dome camera suspended using 3/4 inch emt and set screw connectors. The attachment to the structure is either a blank on a 1900 box punched for a emt connector or a swivel mount plate that you would use for high bays. I get very picky when suspending equipment over peoples heads and this just irks me. I have actually seen one snapped off at the ceiling in Charlotte hanging by only the coax conductor. I am more concerned about this improper use of fittings than the whole ridgid coupling debate.
Jacob
mdshunk said:I see a similar arrangement for suspended exit signs from time to time. I do the same installs, but with RMC or IMC down rods and jack chain for a safety chain on the exit signs. You can split a set screw fitting sometimes by cranking the set screw too hard sometimes. I certainly wouldn't want to rely on its mechanical strength to support something.
georgestolz said:Uh, Joe, I agree with what they've posted and I'm not been approached or brainwashed by the moderators.
<big snip>
joe tedesco said:Could be called: Mix and Match. Fittings shall be permitted to be used anyway you want as long as they work.
iwire said:I disagree, nothing has been presented from the NEC, NEMA or UL that prohibits this practice.
It is simply a practice that Joe does not like.