........., I called to see what NEC code they are on. They said 2009 yikes..........
I'd like to see a 2009 NEC.
........., I called to see what NEC code they are on. They said 2009 yikes..........
Yeah, me too. It raised my internal red flag. But the entire house electrical was done exactly by code.....I'd like to see a 2009 NEC.
I've had 'em tell me 2012, 2018, etc.I'd like to see a 2009 NEC.
No plastic insulation on the staples?Show him this new product from Madison (Now Southwire). This will make his head spin. https://www.google.com/search?q=southwire+mwt1&sxsrf=ALeKk003cdAGyYGLubcoOQHF5em0XSEm0Q:1619396047639&tbm=isch&source=iu&ictx=1&fir=p0KtvJntANeSxM%2C_gSRfgeCSGYhnM%2C_&vet=1&usg=AI4_-kRqQPRNj0RBzvRXyAeOaOYW-UMOuA&sa=X&ved=2ahUKEwiVwq2x0JrwAhVCIDQIHdq-BGcQ9QF6BAgOEAE&biw=2197&bih=943#imgrc=p0KtvJntANeSxM
I don't know why anybody would ever use staples with plastic.No plastic insulation on the staples?
Because they are easier to drive and also prettier!I don't know why anybody would ever use staples with plastic.
So leave the long length as many do, but put a pancake box (temporarily for inspection) on the end and off to one side of the vanity area. See if they say anything about that being an unusual location or notice that light is in different place at final inspection.In Polk County they not only want a box ,the wire has to be stripped and the ground must be attached on the box if it's a pancake or metal box . It is stupid in my opinion because most of the time the exact location of the wire ends up having to be moved. If it's just a wire you can just make a small notch but if there is a box now you have drywall patching . Most inspectors try to use common sense but you will always have a few idiots that do not know what they are doing . Unfortunately you might as well just do what they want because it will just get worse even if you prove them wrong .
So leave the long length as many do, but put a pancake box (temporarily for inspection) on the end and off to one side of the vanity area. See if they say anything about that being an unusual location or notice that light is in different place at final inspection.
Slack NM cable run between studs for the future installation of a box for a light. Will be covered up by sheetrock, then an old-work box installed at trim.
What I would do is slap a box up, stuff the end in, let the inspector pass it, then pull the box off the stud and zigzag it back to where you want it.
That been like three weeks ago and already forgotten aboutSounds familiar.
Zigzaging the wires or a little loop where you think the box will be near is how electricians have done bath vanity light rough-ins for very many years and still do today.I don't know that zigzagged wires are really supposed to be approved, either. The book mentions wires run alongside and parallel to framing members, and bored through holes.
Really, I think it just comes down to a need for better planning. I have two remodeling contractors who used to insist I just leave a wire in the wall and yse a cut-in box later. I told them both to take a hike. Get me a center measurement and I'll make sure it's exact.
Sometimes they like to say the customer doesn't know what they want yet. My reply is that I shouldn't be wiring something if they don't even know what the heck they want. Get a plan before the work gets done. It's not that hard
Liked - But it is not in the NEC . that's my point. Not nationally and not in this jurisdictions local amendments.I was in the field for 22 years then became an inspector.
I would definitely approve a coiled cable at rough and check for full compliance at final.
The new code makes no sense to me.
Ron
314.23(C) specifically allows a box mounted in a finished surface by clamps, anchors, or fittings identified for the purpose. No mention of when permited to use. If there was one it would be there I would think.Thanks for asking. He said that was alright with cat flex. His concern is the boxes.
He thinks the NEC says " No Renovation boxes allowed on new construction"
I told him to show me in the NEC or in local amendments. He got mad.
I've had both that are a pain. But generally the one that has been there and done that is the one you want, they might even have a suggestion on what works good and is also code compliant in a few cases.Question, Preference, You want an inspector who's been there, done that, who has worked in the trade, or one that only read the book? Which is a bigger pain? Pros, cons?
This is great Fred, exactly what I was looking for. This proves my point. ThanksI didn't see a specific code section# the inspector said was violated?
314.23(C) specifically allows a box mounted in a finished surface by clamps, anchors, or fittings identified for the purpose. No mention of when permited to use. If there was one it would be there I would think.
Though not normally a problem in a single family dwelling, I believe boxes in a wall that requires a fire rating must be supported by something other than the wall covering or something to that effect. Wall between garage and house maybe where you might run into this the most in a SFD, but not where I am. Many just have OSB on the garage wall - no building inspectors though. I have OSB on mine, but there is 5/8 rock behind it.I didn't see a specific code section# the inspector said was violated?
314.23(C) specifically allows a box mounted in a finished surface by clamps, anchors, or fittings identified for the purpose. No mention of when permited to use. If there was one it would be there I would think.