Several comments:
1) Here is a link to Hoffman/PentAirs panel heat calculator: https://coolingtool.pentairprotect.com/index.html
2) Depending on the HP size of the VFD's, I'd also be concerned about the amount of noise, EMI, EMF, or whatever you want to call it interfering with things, especially if you'll also be installing line reactors or filters inside of the panel too.
3) I've seen panels with large drives be modified so the drives' heat sinks are cut out thru the back of the panel, thus most of the heat is effectively exhausted.