when I was an apprentice my boss told me he better never see me put romex (with Its Jacket) into an emt conduit as you would with normal individual insulated wires. I assumed this was a code violation at that time.
However, after reading NEC years later I found that there are situations romex is to be protected by a steel sheet atleast 1/4” thick or When entering a floor hole to be protected by a metallic conduit sleeve.
I have also not found a code (not mentioning fill limit code) that specifically says romex cannot be put Into EMT or conduit. Is this correct?
I also recently passed romex through a double gang metallic box without breaking wires out of jacket, straight in left to exit rear. Code requires equipment to be bonded if likely to be energized but since the conductors are insulated in their Factory jacket, would you still need bonding here?
However, after reading NEC years later I found that there are situations romex is to be protected by a steel sheet atleast 1/4” thick or When entering a floor hole to be protected by a metallic conduit sleeve.
I have also not found a code (not mentioning fill limit code) that specifically says romex cannot be put Into EMT or conduit. Is this correct?
I also recently passed romex through a double gang metallic box without breaking wires out of jacket, straight in left to exit rear. Code requires equipment to be bonded if likely to be energized but since the conductors are insulated in their Factory jacket, would you still need bonding here?