And you misunderstood what the video is saying. When posting here on the forums you need to have your code book with you, that way you can follow what the others are telling or asking you.Mike holt also has a video on this
And you misunderstood what the video is saying. When posting here on the forums you need to have your code book with you, that way you can follow what the others are telling or asking you.Mike holt also has a video on this
Like I said my code book is at work, I do not carry it around with me everywhere I go and on my days offAnd you misunderstood what the video is saying. When posting here on the forums you need to have your code book with you, that way you can follow what the others are telling or asking you.
I wouldn't expect you to carry it everywhere but when you make statements or someone points you to an answer here on the forums you should have it to reference.Like I said my code book is at work, I do not carry it around with me everywhere I go and on my days off
Think about that for a minute...that would make absolutely no sense.But nec says you cannot terminate a conductor with a higher temperature rating than the temperature rating of the point or component of termination unless for cases of ampacity adjustment derating on the conductor
If Victorville is Victorville, CA, you can read the NEC as adopted and modified by CA here. This is the 2022 CA Electrical Code, based on the 2020 NEC, which doesn't go into force until January 1, 2023, I believe:Like I said my code book is at work, I do not carry it around with me everywhere I go and on my days off
O I see ok so nec 2022 is not effective until Jan 2023 California. So by reading this code book I’ll be aheadIf Victorville is Victorville, CA, you can read the NEC as adopted and modified by CA here. This is the 2022 CA Electrical Code, based on the 2020 NEC, which doesn't go into force until January 1, 2023, I believe:
California Electrical Code 2022 based on the NFPA 70, 2020
UpCodes offers a consolidated resource of construction and building code grouped by jurisdictionup.codes
You can also read it at nfpa.org with a free account, but their interface is intentionally less user friendly.
Cheers, Wayne
Think about that for a minute...that would make absolutely no sense.
So the breaker rating determines if said conductor can be used since breaker ultimately reduces or limits ampacity?But there's an important difference in emphasis: more commonly you'd say "when a 90C rated conductor is terminated on a 60C rated terminal, you are limited to the 60C termination temperature ampacity." "You are limited to" is the same as "you can't do it unless." The latter is just discordant as it suggests that normally you can't do it, when it's done all the time.
Cheers, Wayne
No. The breaker temperature rating is a limit on the final circuit ampacity. Nearly all the conductors you ever use have 90C insulation these days, and it's never a problem to have a conductor insulation temperature rating higher than the minimum required.So the breaker rating determines if said conductor can be used since breaker ultimately reduces or limits ampacity?
No, the lowest temp rating in the chain be it the termination, splice, breaker, receptacle, switch, conductor, etc... determines the maximum all can be used at. If one component is 60 deg everything else in the chain can be 90 deg rated but they can not exceed 60 degSo the breaker rating determines if said conductor can be used since breaker ultimately reduces or limits ampacity?
Nobody has said or implicated that.Or are you saying it can be done in disregard of code or is done often?
Your not understanding as the statement makes perfect sense. I’ll try to explain it another way. If the conductor is rated 90 degrees Celsius and you are terminating on a breaker rated 60 degrees Celsius, mr. mike holt said this could not be done unless the wire is deranged to the ampacity of the wire conductor of the 60 degree rating.
That's not quite correct. Take the two examples I gave. In the second example, with 4 CCCs, the conductor temperature at that location might exceed 60C. That's why it would need to have at least 75C rated insulation.No, the lowest temp rating in the chain be it the termination, splice, breaker, receptacle, switch, conductor, etc... determines the maximum all can be used at. If one component is 60 deg everything else in the chain can be 90 deg rated but they can not exceed 60 deg
That’s what I was thinking but mike holt has made more confusion on thisNo. The breaker temperature rating is a limit on the final circuit ampacity. Nearly all the conductors you ever use have 90C insulation these days, and it's never a problem to have a conductor insulation temperature rating higher than the minimum required.
Cheers, Wayne
Wayne, that is not what is confusing the OP and thanks for making it more confusing for him.That's not quite correct. Take the two examples I gave. In the second example, with 4 CCCs, the conductor temperature at that location might exceed 60C. That's why it would need to have at least 75C rated insulation.
Cheers, Wayne
Sometimes simple to the point answers are the best.The company I work for only buys THHN but according to code this 75 degree wire is too high for typical installations? Such as terminating on standard 15 to 20 ampere receptacles? Even with ampere derating, what kind of wires should be bought for 60 degrees?