Naplessparky2965
Member
My inspector will not let us pull wire until all the outside windows and doors are installed. Is there somewhere in the Code or a change that gives him the authority to do this.
110.11 Deteriorating Agents.
Unless identified for use in the operating environment, no conductors or equipment shall be located in damp or wet locations; where exposed to gases, fumes, vapors, liquids, or other agents that have a deteriorating effect on the conductors or equipment; or where exposed to excessive temperatures.
FPN No. 1: See 300.6 for protection against corrosion.
FPN No. 2: Some cleaning and lubricating compounds can cause severe deterioration of many plastic materials used for insulating and structural applications in equipment.
Equipment not identified for outdoor use and equipment identified only for indoor use, such as ?dry locations,? ?indoor use only,? ?damp locations,? or enclosure Types 1, 2, 5, 12, 12K, and/or 13, shall be protected against permanent damage from the weather during building construction.
Naplessparky2965 said:My inspector will not let us pull wire until all the outside windows and doors are installed.
Naplessparky2965 said:My inspector will not let us pull wire until all the outside windows and doors are installed.
OP wanted a code reference so he got one.:grin:infinity said:"Permanent damage" is highly ambiguous to say the least
and does 110.11 apply to conductors?
Rob, I'm not saying this is a big deal down here, only that an inspector might choose to use this in certian conditions.have a deteriorating effect on the conductors or equipment
chris kennedy said:Rob, I'm not saying this is a big deal down here, only that an inspector might choose to use this in certian conditions.
Sure why not according to 110.11.infinity said:So if I'm using a conductor listed for wet locations I'm good?
growler said:Why would you want to pull wire before all windows, doors and maybe a security system are installed? :grin: :grin:
Naplessparky2965 said:The roof is completely dried in and the stucco guys are putting stucco on the walls. We are having to mount all our boxes on the outside but not able to pull the wire.
peter d said:I agree, copper theft is reason enough alone not to install wiring without the building being secure.
Sierrasparky said:it's not the inspectors job to secure a jobsite. It's the Owner or the GC.
Unless the job is in a severly damp climate I don't see the justification.
There is plenty of wires to be pulled prior to windows and doors. Doing this could prevent the EC from completing rough in a timly manner.
I'd call his boss. That code section does not fly with me.