chevyx92
Senior Member
- Location
- VA BCH, VA
cowboyjwc said:Here the minute the walls are framed you can start pulling wire.
Even with no roof?
cowboyjwc said:Here the minute the walls are framed you can start pulling wire.
cowboyjwc said:Here the minute the walls are framed you can start pulling wire.
cowboyjwc said:Here the minute the walls are framed you can start pulling wire.
chevyx92 said:I don't think the code section you don't agree with cares about time. It hads to do with keeping the integrity of the premise wiring. IMO.
Sierrasparky said:If there is a roof on the job and the climate does not present a damp issue I don't think there is a darn thing he has to say.
110.11 Deteriorating Agents
So again unless there is and issue relating to dampness. Window's and doors will not prevent coorosion from vapors. I can understand not having a panels bus installed untill after drywall. I do that anyway. That same Inspector could use the issue of temperature in Arizona in the summer. What then you're gonna tell the GC he cant wire the place untill the AC is on.
I'd tell that guy to go pound sand.
chevyx92 said:Well no, I agree with you if the enviornment like Arizona was the situation. But other states would vary, I guess it's where you live or the job in question is at.![]()
Sierrasparky said:So does this mean you need to throw away a roll of romex cause it was in the back of your truck and it rained?
ultramegabob said:there is a saying where I live, "If you dont like the weather, stick around a few minutes it will probably change" it can be sunny, and out of nowhere get dark and rain like crazy, and then be sunny again in no time flat around here.
Location, Dry. A location not normally subject to dampness or wetness. A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction.
I had an inspector, years ago, challenge me on this issue and I told him exactly what Roger stated above. It is a normally dry location. He complained but let it slide but called me a damn yankee before he left. :grin:roger said:The way I see it, we're talking about a dry location, especially with the roof being in place and the inspector is just holding up the job.
[/color]
I believe Southwire has a paper that backs this up for NM.
Roger
roger said:The way I see it, we're talking about a dry location, especially with the roof being in place and the inspector is just holding up the job.
[/color]
I believe Southwire has a paper that backs this up for NM.
Roger
mpd said:I would have no issue with the windows, what I would have an issue is are they all done framing, we had to stop a development because after the rough elec. was passed the framing crew would go back in and start installing blocking, and if the wiring was in the way it got smashed, nailed or cut, no choice but to slow them down
donselectric said:but it is a violation...
ItsHot said:Since some new homes are being wired two and three times over due to copper theft, I think this is the concern in seeing that the structure can be secured.