I was ask to look at this and comment. Sent to me from an apprentice that I had worked with. He told his journey man that it did not look correct and was told not to bother him any more about it. He told me it just did not look right.
With out giving to much info see if you can see what wrong.
It took me a minute to figure out what they did based on pic than I ask a few questions.
This is a service entrance rated transfer switch being used as one.
400 amp three phase 120/208 wye.
The green wires are a #4. I used word green as not to give it away right off the bat.
The parallel sets are 3/0 cu.
The single set is 500 mcm cu.
I told him to have his boss explain it to him.
To answer his question it wrong, red tag big time, epic fail.