Roger his is not the thread I was talking about but it fits fine.
Cramp like this is the reason most people in this trade burn out every 12 or so years after being in the trade.
Myself I have burned out at least three times.
This is the most debatable subject, other than grounding I guess that is argued about in the trade and very confusing.
The thread I was talking about the main was more like 35 ft. from the indoor panel thats why I got a kick when you called them buss extensions instead of conductors I know your statement was in fun.
But really wouldn't the answer depend on where you are bonding your neutral and grounding electrode conductors together?
Since the NEC says bond as close to the main as possible I think the load center should be treated as a sub panel with a four wire feeder.
But if the inspector allows you to bond them in the load center and take your grounding electrode conductor to the electrode from the load center to the electrode then you would need three conductors two hot and a neutral from the main outside too the load center in side.
If you bond the neutral and ground together in the main outside then from that point on you should separate your neutral and ground.And you would need two hots one neutral and Equipment grounding conductor.
If I am repeating what someone else has already said I apologize and agree with you.
Ronald