At CMP-12 today's big topic is compatibility of bath fans with AFCI,
in support of expanding AFCI devices to bathrooms, by ACMBA (American Circuit Breaker Manufacturer's Association).
-
And testing results in support of AFCI expansion to attics, despite the difficult temperature and humidity environment in many attics.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Yes, and they can change their vote, so influence or information after the public input can sway the vote in theory.
Yes the votes at the meeting are not final...not even sure if they record anything other than the numbers at the meeting. When the final ballot is published, you can see how each panel member voted. Also as part of the ANSI consensus standard rules, all negative votes must have a comment. If there is no comment with the negative vote, that vote won't be counted.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
At CMP-12 today's big topic is compatibility of bath fans with AFCI,
in support of expanding AFCI devices to bathrooms, by ACMBA (American Circuit Breaker Manufacturer's Association).
-
And testing results in support of AFCI expansion to attics, despite the difficult temperature and humidity environment in many attics.
While I am not a supporter of the AFCI rules, unless the AFCI itself is installed in the difficult temperature and humidity environments, I don't see that as an issue.
 