Okay. I'm good with you doing this. I work on enough different stuss that I have not seen a need for this constraint.winnie said:When solving these problems, I tend to stick with the _same_ set of sense designations rather than switching for different problems. ...
I'm translating this as generalized to 3ph grounded Wye. Again okay.winnie said:... I stick with the source neutral as the voltage reference, and use 'current flowing _out_ of each source terminal' as my current sense....
Ah - This is why I guessed the above quote was generalized to grounded Wyewinnie said:... But I find that it makes life easier when solving for (say) multiple loads connected to a wye source. ...
This one baffled me for a while. But maybe I got it now. You are differentiating between a KVL solution where the current is in a loop - vs a KCL solution where the currents sum to zero at a node. For example, KCL at a node: Iin -Iout = 0 Hence the perception that the current swapped sense (direction? description?). Is this correct?winnie said:... In the single phase center tapped system, the same current is flowing through the entire system. There is _no_ change in the current flow as it passes through the neutral point. The only thing that changes is the _description_ of the current flow. ...
I will have to think about this a bit. It's pretty rare that I am concerned with generator power out and load power in in the same breath. But I think you are saying: Pgen - Pload = 0 Which as simplistic as that sounds, does come up when one can get into a suituation where the gens are exporting vars to a utility (and that one has come up once)winnie said:... You want to describe your voltages and your currents using the same 'sense', so that when you multiply current times voltage you get a positive number for components that supply power, and a negative number for components that consume power. ...
Again, I'm translating this as generalized to multi-phase grounded Wye - which isn't what we are dealing with.winnie said:... If you elect to describe all of your voltages relative to the neutral point, then the sense that you use to describe current must also be oriented with the neutral point. If (as I do) you always describe current in terms of the flow _out_ from the neutral along the various branches of the circuit, then the sign or phase of the _description_ of the current flow will flip as you go through neutral. This change in description of the current matches the description of the voltage, and maintains the convention that (voltage * current) is power supplied by that component ...
Excellent geography lesson. I'll keep it in ming next time I drive through North Pole (I do that a few times a month:smile: