Originally posted by georgestolz:
Okay, there two ways of looking at this. The NEC, and the "real world."
According to the NEC, the section that Dillon posted, is that the appliance garage receptacles cannot be considered as meeting the spacing requirements for the countertop beside it. So inside the appliance garage (or AG for short, here) is not countertop space.
Therefore, feeding that outlet with an SA circuit is illegal. According to 210.52(B)(1), the SA circuits are for meeting wall space codes, and counter space codes. A receptacle inside a cabinet is not serving counter or wall spaces.
I knew, I should have let this thread pass me by..
*illegal to count as SA circuit,not so fast here..
210.52(B)Receptacle outlet served.
(1)In the kitchen,pantry,breakfast room,dinning room, or simular area of a dwelling unit,the two or more 20-ampere SA branch circuits
required by 210.11(C)(1) shall serve all wall and floor receptacle outlets
*covered by 210.52(A),* all countertop outlets
covered by 210.52(C) and receptacle outlets for refrigeration equipment.
*forgive me for skipping typing the Exceptions of 1 & 2.
210.52(C)(5)-Receptacle outlets rendered not readily accessible by appliances fasten in place,appliance garages,sinks,or rangetops as covered in 210.52(C)(1),Exception,or appliances occupying dedicated space shall not be considered as required outlets*exceptions to (5)
*if you can not comply in this exceptions,does this mean if you install receptacle outlet in *appliance garage
(which is not required), will this relieve you of the responsibility of the SA circuit requirement of this outlet,if excluded from the
required counter wall space?
..Nope..I don't believe it relieves you of the SA circuit requirement.
[ September 24, 2005, 01:29 PM: Message edited by: dillon3c ]