Re: Kitchen circuits
George you are talking receptacles and I am talking circuits these are two different things.
{QUOTE] 210.52 (B) Small Appliances.
(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit,
the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A),
all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment. [/QUOTE]
According to the rules of English (and I know you know these) the comma ends one thought and begins another. The rule 210.52 (B)(1) could be read like this as it would pertain to countertops. (1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit,
the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all countertop outlets covered by 210.52(C),
You are saying that a receptacle rendered inaccessible by the appliance garage does not count and I agree.
I am saying that any receptacle that is no more than 20 inches above or more than 12 inches below the top of that counter is required to be protected by the small appliance circuit no matter where you place it.
To carry this conversation a step future, should the entire countertop be enclosed with an appliance garage then I wound contend that receptacles would be required to be installed to serve the counter top by some other means.