210.52(B)(1) says the wall, floor, and countertop receptacles "In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit" shall be supplied by the SABCs. The exception just says you can have an additional circuit serving a receptacle, when that receptacle is switched per 210.70(A)(1) Exception 1 in lieu of a lighting outlet. The latter exception excludes kitchens, but the 210.52(B)(1) exception would apply to "pantry, breakfast room, dining room or similar."But 210.70(A)(1) exception clearly indicates that it (210.70(A)(1) exception no.1) doesn't apply to kitchen and bath receptacles. The required receptacles in a kitchen is the SABC, thus the switching seems to be not allowed.
Thus the exception in 210.52(B)(1).
None of that has any bearing on whether SABCs can be switched. 210.52(B)(1) is only about which circuits may serve which receptacles.
The language of that section would not apply to manual switch control.The requirements of 406.3(E) to be "permanently marked with the symbol shown in Figure 406.3(E) and the word "controlled"."
Cheers, Wayne