Nowhere does the Code say switched receptacles on SABCs are not permitted.By inference, it does prohibit what is not permitted
Nowhere does the Code say switched receptacles on SABCs are not permitted.By inference, it does prohibit what is not permitted
There is no prohibition on switching SABC receptacles in this quoted text.I agree - appliance circuits cannot be switched
210.52(B) Small Appliances.
210.52(B)(1) Receptacle Outlets Served.
Exception No. 1: In addition to the required receptacles specified by 210.52, switched receptacles supplied from a general-purpose 15- or 20-ampere branch circuit as required in 210.70(A)(1), Exception No. 1, shall be permitted.
It does, by inference, when it says they are allowed in those other scenarios.Nowhere does the Code say switched receptacles on SABCs are not permitted.
By inference, it does prohibit what is not permitted
It does, by inference, when it says they are allowed in those other scenarios.
I'll give you an example from a different context
(only to make the specific point).
We are going into stores now and seeing signs which say people who are vaccinated are allowed to enter without a mask.
There is no prohibition on switching SABC receptacles in this quoted text.
An outlet containing a duplex receptacle that is wired so that only one of the receptacles is controlled by a wall switch can be used to meet the receptacle outlet spacing requirement. However, if both halves are controlled by a wall switch or other wall-mounted control device, such as an occupancy sensor, an additional unswitched receptacle has to be installed to meet the receptacle outlet spacing requirement. Where both halves of the duplex receptacle are controlled by a wall switch, the occupant could run an extension cord from a receptacle that is not controlled by a switch to an appliance that requires continuous power.
Inference is inferer-dependent. Thus, inference is not enforceable.We are going into stores now and seeing signs which say people who are vaccinated are allowed to enter without a mask.
The very clear inference is that if you haven't been vaccinated, then you you are prohibited from entering unless you wear a mask. It doesn't have to be spelled out in black and white to see the inference.
I don't believe that's correct. The start of 210.52 says that a switched receptacle provided in lieu of a lighting outlet under 210.70(A)(1) Exception 1 may not count towards the 210.52 requirements. But if you choose to switch it for some other purpose, nothing in 210.52 says it doesn't count.No there isn't but if you switch the small appliance branch circuit then you do need to install another receptacle to meet code requirement for the small appliance branch circuit.
That doesn't say that the SABC receptacles can't be switched. It is an exception to 210.52(B)(1) which says that all the subject receptacles shall be served by the SABCs. The exception allows a receptacle on a non-SABC, if it is a switched receptacle installed in lieu of a lighting outlet per 210.70(A)(1), Exception No 1. Since that latter exception doesn't apply to kitchens, the 210.52(B)(1) Exception is only relevant for dining rooms.I agree - appliance circuits cannot be switched
210.52(B) Small Appliances.
210.52(B)(1) Receptacle Outlets Served.
Exception No. 1: In addition to the required receptacles specified by 210.52, switched receptacles supplied from a general-purpose 15- or 20-ampere branch circuit as required in 210.70(A)(1), Exception No. 1, shall be permitted.
Did you read the comment made by the cmp.I don't believe that's correct. The start of 210.52 says that a switched receptacle provided in lieu of a lighting outlet under 210.70(A)(1) Exception 1 may not count towards the 210.52 requirements. But if you choose to switch it for some other purpose, nothing in 210.52 says it doesn't count.
Cheers, Wayne
However, if both halves are controlled by a wall switch or other wall-mounted control device, such as an occupancy sensor, an additional unswitched receptacle has to be installed to meet the receptacle outlet spacing requirement.
You mentioned that text is available as "part of the 2020 version," where exactly?Did you read the comment made by the cmp.
Don't know exact wording of 2020 but in 2017 the quoted text no where states "in accordance" but says that "as defined in ....." text quoted above. The defined receptacle is done for lighting "in lieu of lighting outlet(s)". This appears a switched outlet is only for use as a lighting outlet, and as an allowance given the "No other outlet" requirement to follow in:You mentioned that text is available as "part of the 2020 version," where exactly?
Anyway, if that is what the CMP intends, then they need to delete "in accordance with 210.70(A)(1), Exception No. 1" from 210.52(2). What is currently written in the NEC obviously does not match the commentary.
Cheers, Wayne
In my opinion and others', that's to allow additional circuits, not additional switches.Larry, I see your point of "permissive code" but If 210.52(B)(1) receptacles were allowed to be switched why give the exception?
210.52(B)(1) Exception No. 1: In addition to the required receptacles specified by 210.52, switched receptacles supplied from a general-purpose branch circuit as defined in 210.70(A)(1) Exception No. 1, shall be permitted.
That's to prohibit lighting on the SABC circuits, to minimize risk of a light outage amid malfunctioning hot appliances.Don't know exact wording of 2020 but in 2017 the quoted text no where states "in accordance" but says that "as defined in ....." text quoted above. The defined receptacle is done for lighting "in lieu of lighting outlet(s)". This appears a switched outlet is only for use as a lighting outlet, and as an allowance given the "No other outlet" requirement to follow in:
"210.52(B)(2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets."
Again, if the SABC is allowed to be switched, there would be no need for the addition of the exceptions.
I was quoting 210.52(2), not (2017) 210.52(B)(1) Exception 1.Don't know exact wording of 2020 but in 2017 the quoted text no where states "in accordance" but says that "as defined in ....." text quoted above.
The only thing that comes to mind is the temptation to plug in lights.What is the exact problem being prevented by prohibiting such additional switching.
But 210.70(A)(1) exception clearly indicates that it (210.70(A)(1) exception no.1) doesn't apply to kitchen and bath receptacles. The required receptacles in a kitchen is the SABC, thus the switching seems to be not allowed. Thus the exception in 210.52(B)(1).In my opinion and others', that's to allow additional circuits, not additional switches.
That's to prohibit lighting on the SABC circuits, to minimize risk of a light outage amid malfunctioning hot appliances.
And most if not all lamps are not corded for 20 amp circuits. (Required for the SACB)The only thing that comes to mind is the temptation to plug in lights.
You mentioned that text is available as "part of the 2020 version," where exactly?
Anyway, if that is what the CMP intends, then they need to delete "in accordance with 210.70(A)(1), Exception No. 1" from 210.52(2). What is currently written in the NEC obviously does not match the commentary.
Cheers, Wayne
True, but 20a receptacles are not required, and they accept 15a plugs.And most if not all lamps are not corded for 20 amp circuits. (Required for the SACB)