- Connecticut
- Engineer
But I can’t find anything that says these outlets can not be switched.
I agree...I don't see any language that would prohibit switching the countertop receptacles.
210.52 Dwelling Unit Receptacle Outlets. This section provides requirements for 125-volt, 15- and 20-ampere receptacle
outlets. The receptacles required by this section shall be in addition to any receptacle that is:
(2) Controlled by a wall switch in accordance with 210.70(A)(1), Exception No. 1
210.70 Lighting Outlets Required. Lighting outlets shall be installed where specified in 210.70(A), (B), and (C).
(A) Dwelling Units. In dwelling units, lighting outlets shall be installed in accordance with 210.70(A)(1), (A)(2), and (A)(3).
(1) Habitable Rooms. At least one wall switch–controlled lighting outlet shall be installed in every habitable room and bathroom.
Exception No. 1: In other than kitchens and bathrooms, one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets.
I don't have them in an electronic format and am not going to scan them. You can look around for the archived information for the various editions of the NEC at www.nfpa.org/70. I think you have to go back to the 96 or 99 code.Could you post a copy or link to the substantiations and comments?
I don't see any language that says you cannot switch the small appliance branch circuit receptacles.The receptacles can be switched but the small appliance branch circuit receptacles cannot be switched. You can add a switched receptacle as long as you satisfy 210.52 requirements first
You got me there Larry. I forgot about that.How about a 2p switch?
Oops. I didn't know this. About a year back I used six two-pole switches to control 12 lighting circuits in a store. They were using non-switch-rated circuit breakers to control the lights and wore a couple of them out. I had to replace all twelve circuit breakers as well.It it is marked for 2 circuit operation, that is fine (assuming you are permitted to switch these receptacles). The UL Guide Information for Snap Switches (WJQR) says this:
Maybe that is what the cmp intends, but the language doesn't say that.
As a permissive code, the NEC permits that which it doesn't prohibit.If SABC can be switched why add an exception that would allow adding another circuit into the space and those receptacles can be switched?
I agree - appliance circuits cannot be switchedMy reading of 210.52(B) would indicate that the 2 required 20A SABC would have to be unswitched given the exception #1 specifically allows for the addition of switched receptacle(s) from a general purpose branch circuit.
Terminology is everything if you read it correctlyAs I read it, there is a requirement that all receptacles in a kitchen be SABCs. There is an exception to this requirement, permitting a switched general purpose receptacle. So you can't have an unswitched _general purpose_ receptacle in a kitchen. But this doesn't say anything about switching of the SABC receptacles.
IMHO SABC receptacles may be switched, and in fact commonly are switched. The SABCs in my kitchen are switched, along with every single other circuit in my home. The switches also function as the required overcurrent protection for the circuits, but then again I am a DIY hack.
As far as why someone might want to do this, presumably it adds some measure of safety. I recently purchased an 'air fryer' and the instructions specifically state " UNPLUG FROM OUTLET WHEN NOT IN USE AND BEFORE CLEANING. Allow to cool before cleaning or handling, putting on or taking off parts. " https://images-na.ssl-images-amazon.com/images/I/C1XPryhvcuS.pdf which given that the plug is behind the unit is rather annoying. I'm considering a switched outlet as an alternative to simply ignoring the instructions.
-Jon
??????????"Shall be permitted" does not exclude all else.
Reference to post #31.??????????
210.70(A) (1) has nothing to do with the kitchen.I agree - appliance circuits cannot be switched
210.52(B) Small Appliances.
210.52(B)(1) Receptacle Outlets Served.
Exception No. 1: In addition to the required receptacles specified by 210.52, switched receptacles supplied from a general-purpose 15- or 20-ampere branch circuit as required in 210.70(A)(1), Exception No. 1, shall be permitted.
That's what I'm sayin'.A particular type of switched receptacle 'shall be permitted'. This does permission does not prohibit any other sort of switched receptacle.
By inference, it does prohibit what is not permittedA particular type of switched receptacle 'shall be permitted'. This does permission does not prohibit any other sort of switched receptacle.
-Jon
But I still don’t see where it says it isn’t permitted.By inference, it does prohibit what is not permitted