Re: Kitchen island receptacles
Originally posted by jim dungar: 210.52(A)(2)(2) does specifically require you to include the fixed panel of a sliding door when determining wall space.
No it doesn't. Look again. The word "door" does not appear in that paragraph. It is talking about solid walls, and it is specifically excluding any type of panel (glass or wood or whatever) that slides.
On the other hand, the word "door" (actually "doorways") does appear in 210.52(A)(2)(1).
Originally posted by jim dungar: 210.52(A)(2)(3) says a counter type room divider must be also be included.
For the moment, I will not argue against that point. But I'll not concede it either. I have two problems with the way that article is worded.
One problem is that I don't know what "afforded by" means. Here's an example:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Suppose you have a "Great Room" with a wall 20 feet long, and with doorways at both ends of that wall. You need a minimum of 3 receptacles for that wall. You can put one in the middle, and one 6 feet from either end of the wall.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">But suppose you install a railing that extends (let us say about four feet) into the room from the midpoint of that wall. Build it with fancy dowels and a top rail, but do not use a flat vertical surface that could in any way resemble a wall. You now have a "fixed room divider." My question is this: What is the "space afforded by" that fixed room divider? Is it the space physically occupied by the railing itself? Does that mean that there must be a receptacle on or near the railing (perhaps a floor receptacle)? Many would say "yes." I say "no."</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">I submit that the "space afforded by the fixed room divider" could instead mean the 10 foot wide section of wall to the left of the divider, and it is also the 10 foot wide section of wall to the right of the divider. If that is what it means, then those two areas now only need one receptacle each, for a total of two along that whole wall (instead of the original total of three).</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
My other problem with the wording of that article is that it gives only two examples, and they are not representative of what might be included in the rule. Specifically, I would not place a "peninsula" or an "island" in the same set that starts out with "free-standing bar-type counters" and "railings." Others would include them in that set.
That is why I am not conceding that point just yet.
Originally posted by jim dungar: I see nothing in the code that prohibits receptacles from being installed that are beyond the distances of 12" down and 6" back, as long as 210.52(C)(2) or (3) has been met with at least one receptacle.
I do.
210.52(C) says "receptacles
shall be installed in accordance with (1) through (5). That means that the rule applies to all receptacles that you plan to install in those areas. That does not give you the option of installing extras in that same area in any location or manner that you wish. If the receptacle is in that area, it must follow the rule.