210.52(B)(1) requires all receptacles in the areas defined to be on the SABCs. If it is a receptacle in these areas, it's required to be on those circuits. If you add another receptacle from a non-SABC circuit in those areas, then exception 1 only allows it for a receptacle outlet replacing a lighting outlet required in 210.70, as allowed by exception 1 of that section.
http://forums.mikeholt.com/showthread.php?p=539713#post539713
I recognize that what's throwing a wrench into the works is that once a light is plugged into that countertop receptacle outlet then it suddenly can be called a "lighting outlet" - but a basic rule of sanity is that the end user cannot create a code violation by plugging in an appliance. Otherwise, we'd never be able to leave the house; we'd have to walk around making sure people didn't use blow dryers on their 15A circuits, etc.
If someone's really bored, there was a thread about this topic in the past, I didn't check to see what the verdict was that time, this morning.
Seriously, buddy, you're killing me. Once or twice, it was mildly amusing, now it's just getting old. :roll:frizbeedog said:Frizbeedog just made poo poo on the rug.
No.stickboy said:Would it be a violation to install a switch to control a receptacle serving the kitchen counter?
I read 210.70(1) exception no.1, but this would not be in lieu of the lighting outlet...
210.52(B)(1) requires all receptacles in the areas defined to be on the SABCs. If it is a receptacle in these areas, it's required to be on those circuits. If you add another receptacle from a non-SABC circuit in those areas, then exception 1 only allows it for a receptacle outlet replacing a lighting outlet required in 210.70, as allowed by exception 1 of that section.
According to a forum poll, 75% of people around here disagree with you.quoqueelectric said:Where the switch goes is the outlet.
http://forums.mikeholt.com/showthread.php?p=539713#post539713
The SABC receptacles are required (by 210.52(B)(1) & (2)) to serve all wall and counter spaces in those areas and nothing else. Exceptions 1 & 2 to 210.52(B)(2) are examples of receptacles not in wall or counter space. They are not available for wall use, they are hidden by either a range or a clock, and so would violate (B)(2) if not allowed by the exceptions.Chevyx92 said:I understood that. Thats why I mentioned 210.52(B)(2) Exceptions 1+2. Read them if you have the book. It mentions RECEPTACLES.....for clocks or gas fired equipment. Definition of Receptacle-----> A receptacle is a contact device installed at the outlet for the connection of an attachment plug. So if they are allowing a receptacle fed from the SABC for a clock or gas fired equipment then thats it. The outlets are intended for small appliances on the countertop. Not undercounter lighting, that transformer is not permitted by 210.52(B)(2). IMHO. :smile:
I recognize that what's throwing a wrench into the works is that once a light is plugged into that countertop receptacle outlet then it suddenly can be called a "lighting outlet" - but a basic rule of sanity is that the end user cannot create a code violation by plugging in an appliance. Otherwise, we'd never be able to leave the house; we'd have to walk around making sure people didn't use blow dryers on their 15A circuits, etc.
If someone's really bored, there was a thread about this topic in the past, I didn't check to see what the verdict was that time, this morning.