Hmmm... lots of little holes in this concept and I have some time off today...
Ok, so its well known that you can reap marked savings from PF correction equipment when you are being billed on KVA demand.
OK, no. First off I have NEVER seen a utility that bills solely on kVA demand. They bill on kWh, then in SOME cases there is a
PENALTY for exceeding an allotted kVA demand. But they do not "bill on" kVA demand. Secondly, "marked savings" is the kind of nebulous fluff terminology you see in a marketing pitch, I differ with what it implies.
There are savings associated with I^2R loss reduction that actually gives you some (1%-2%) savings when installing capacitors on a system to reduce kW
Hmmm... I'd say that value is debatable. If the conductors are properly sized to code requirements and adjusted for voltage drop under full load, then the losses would be very low to start with. I believe that 1-2% would be a stretch.
...but KVA savings can yield up to around 25%.
ONLY if you are being penalized for exceeding your allotted kVA demand . If you are not, the savings are ZERO.
We all know however that PF capacitors are not installed to reduce kW.
That would be your first purely true statement. The reason they are not installed to reduce kW is because... doing so doesn't save enough kWh to make it worth doing!
They are installed to reduce kVA, by adding Vars to the system.
Sort of. Technically they STORE (not "add") the VARs for use at a different point in the cycle to reduce the current necessary to make the motor into a motor. But the VARs are still coming from the line source, that's why they do not save kW.
So, with this being said, does anyone know of or have an excel sheet or program that will let one guestimate those kW savings, taking into consideration distance from motor, impedance, age of equipment, current, etc... I'll gladly pay for it or accept it as a token of friendship.lol
"Those kW savings"? What kW savings? We just established they are not there for worthy consideration, or are you trying to hang your hat on the I
2R loss reductions? If so and they are minimal to start with on a properly designed system, then in my opinion, you are clutching at straws. Do they exist? Yes. Are they worth the cost of installing PFC capacitors
JUST for the purpose of attaining that miniscule reduction in losses?
No.
So are you trying to quantify the SIDE BENEFIT of reducing the I
2R losses from having installed PFC caps to reduce PF penalties? Because THAT is, in my opinion, the only reason to indulge this exercise.
So here are your column headings, solve for each circuit that has PFC caps:
A | Wire size
B | Wire resistance in ohms / ft.
C | Total ckt length in feet from feeder to PFC cap. ***
D | Total circuit ohms
E | Delta I-Load vs I-load wit PFC caps applied
F | I
2R Delta
G | Heat reduction in kW
H | Cost /kWh
I | Operating hours
J | kWh $ saved per circuit
B comes from wire mfr. chart using column A
D = C * B
E = Empirical data from current measurements
F = E
2 * D
G = F x Line Voltage
H = Utility data
I = Empirical data
J = I * H * G
After last circuit Row: sum all of column J
Next row, column J: $ value of your time to do all this, including recording and collecting empirical data
Last row, column J: [Sum of Column J] - [your time cost] = net savings.
*** You have to assume that above the feeder, circuit conductor size increases to the point where the conductor heating delta from the reduction in load becomes so negligible that it cannot be calculated.