btruppel said:I have 2 600w trans and was going to use 10/2 landscape wiring to run from the trans to the fixtures.
A 600 watt transformer is actually two 300 watt loads, 411.2 will only allow 25 amps max on a secondary circuit.
btruppel said:I checked the code book but I can't find anything that indicates this can't be done. The only thing that worries me is that there is a higher amp on the low volt cable and would it be safer to run this in pipe?
As already mentioned 411.4 is the rule you have to follow, also IMO what your doing is a bad design, voltage drop is going to be a huge factor, I would mount the transformers outside on 4x4's behind a tree or bush...