mwm1752
 - Aspen, Colo
210.11 Branch Circuits Required
Branch circuits for lighting and for appliances, including motor operated appliances, shall be provided to supply the loads calculated in accordance with 220.10. In addition, branch circuits shall be provided for specific loads not covered by 220.10 where required elsewhere in this Code and for dwelling unit loads as specified in 210.11(C).
(C) Dwelling Units.
(2) Laundry Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.
(F) Laundry Areas. In dwelling units, at least one receptacle outlet shall be installed in areas designated for the installation of laundry equipment.
So, if you have your laundry branch circuit for the washer which serves as the one required branch circuit -- are you allowed to have a laundry counter top receptacle circuit that also serves the laundry lighting? & is it required to be 20 amp?
(C) Dwelling Units.