gar
Senior Member
- Location
- Ann Arbor, Michigan
- Occupation
- EE
190117-1538 EST
tersh:
I tried several different inductive loads this afternoon, 120 V circuit, and none produced any huge voltage transients. I did not have one of my 8' Slimline fixtures without a line filter to test. None of my test loads produced more than about 20 V.
I am beginning to wonder if your load has some defect causing unwanted leakage current only under turn on or off times.
Does your former college have test equipment and willingness of your professor to study your problem? This would be the best place to do this.
.
tersh:
I tried several different inductive loads this afternoon, 120 V circuit, and none produced any huge voltage transients. I did not have one of my 8' Slimline fixtures without a line filter to test. None of my test loads produced more than about 20 V.
I am beginning to wonder if your load has some defect causing unwanted leakage current only under turn on or off times.
Does your former college have test equipment and willingness of your professor to study your problem? This would be the best place to do this.
.