My company is investigating using a short section of LFMC (flex) in place of an expansion fitting to compensate for expansion and contraction of long runs of EMT conduit on Rooftops. The idea is that this will save cost. I'm not entirely supportive, but we have a few folks pushing the idea.
There are a few concerns:
- the LFMC might sag onto the roof. possible solution is to bend the EMT up a bit at the ends so the curve of the LFMC goes away from the roof, rather than sagging onto the roof
- the LFMC is difficult to bend and so it will build up pressure in the conduits and not releive the strain on the conduit and support system that the expansion fittings are meant to mitigate.
We had one of our subs build a little mock up with a 1" and 3" section. we are thinking it might be more feasible with the 1" because it's easier to bend...
Does anyone out there have experience with this? Thoughts?
Thanks,
View attachment 14109View attachment 14108
I am in the camp of not worrying about expansion. If this is like most flat roof installations, the whole assemble is floating up on the roof on durablocks anyway so its got plenty of freedom to move. Unless you have straight runs that are ridgedly fixed at both ends, I think there is no issue at all. I think you'd be better off having the guys double check that all their fittings are tight vs having them spend time on this. I dont think Ive ever seen gas piping on flat roofs have flex or expansion fittings.....