LFNC Required?

Status
Not open for further replies.
I have a 500amp refrigeration rack piped in with PVC with back to back 90's between the strut rack on the building and the unit. The refrigeration unit is about 5 feet away from the building, the inspector thinks all the conduits with 120v or more should have flexible conduit between the building and unit. I can't find where LFNC is required to be installed. Can anyone help?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If the unit requires flexibility then it would be required. I am not familiar with this unit but it sounds like an authority having jurisdiction call.
 

iwire

Moderator
Staff member
Location
Massachusetts
Unless you are worried about noise and vibration. Which is not likely to be a real problem.

They are all so loud to start with it makes little difference.

Here is a small typical rack, notice it has a firm metal frame that sits directly on the floor.

The indvidule compressors will be on vibration mounts.


bigParallel.jpg
 