The four list items in 517.26 were added for the 2020 code. Here is the substantiation for that addition.
I was looking for that, thank you!
Again, any change in this would rest with the technical committee for NFPA 99. The CMP for the NEC does not have the authority to make the change.
Perhaps. Here is the 2014:
1981 NEC:
1971 NEC:
The NFPA 70, or whom ever set article 517 in creation has always wanted the life safety branch to comply with article 700. I'm well aware of the desire to harmonize, however, even with 4 exceptions much of 700 still holds true in the 2020 NEC. Including this:
While both life safety and critical require mechanical protection, life safety requires fire protection in addition to extensive physical segregation from normal power going beyond keeping circuits in separate conduit.
Its obvious (IMO) the intent is to keep the life safety branch energized during a fire.
Of course nothing such is hinted or required for the critical branch.
However, in the early development of the 1971 addition such was considered (and supported) for the life support branch- even giving the option of combining both branches at the hospital's discretion. But at the last minute this was changed without written record (to my knowledge), so rapidly even the graphic on page 70-333 of the 1971 NEC does not match the emergency system description on page 70-339 of the 1971 NEC.