The '17 will require us to install afci's on any 120V circuitry
and afci is essentially the American equivalent of an RCD
Assuming similar electrical equipment means assuming similar electrical techniques
~RJ~
Personally I would change 210.12 to read like this:
210.12 Protection Against Wiring Defects.
(A) Dwelling Units. All 120-volt, single-phase, 15- and
20-ampere branch circuits supplying outlets or devices installed
in dwelling units shall comply with one or more the following except
where otherwise noted:
1. Each circuit shall have 50 milli amp or less differential ground fault protection provided by a listed and approved device at the branch circuit origin.
FPN: A 5 milli amp ground fault circuit interrupting device at the branch circuit origin is permitted to fulfill the requirements of 210.12 (A).
Exception: Dedicated branch circuits solely providing service for electric heating equipment as specified in article 424, kitchen refrigeration equipment, fire alarms, and dedicated receptacle circuits intended for treadmills shall not be required to comply with 210.12 (A).
2. Dielectric Strength Test. The wiring of each new circuit
shall be subjected to a 10 second, 1000-volt D.C., dielectric
strength test (with all switches closed) between live parts
(including neutral conductor) and the equipment grounding
conductor relative to the circuit being tested for all new homes to
determine compliance with 110.7. This test shall be performed after branch circuits are complete
and with all switches closed.
Exception: Listed luminaires or appliances shall not be
required to undergo or withstand the dielectric strength test.